The question still stands why 4000? 

Duane

----- Original Message -----
From: [email protected] [mailto:[email protected]]
Sent: Saturday, July 19, 2014 08:15 AM Eastern Standard Time
To: [email protected] 
<[email protected]>
Subject: Re: Segue to AHJ's from CPVC Underground

The stance of the AHJ is that their unwritten policy is pumps can only be used 
at 100%. They also believe that 1500 gpm pumps will only produce 1500 gpm, and 
we have to use 2 2000 gpm pumps to get 4000 gpm. They don't think pressure is 
even a factor.

Ron fletcher Sent from my iPhone

> On Jul 19, 2014, at 5:00 AM, "Johnson, Duane (NIH/OD/ORS) [C]" 
> <[email protected]> wrote:
> 
> There are so many things wrong here. But, you may be able to make this work 
> regardless. Did you take your 75% reduction in fire flow based on the fully 
> sprinklered exception in B105.2? If you are starting at 4000 gpm, the 
> required flow can be reduced to 1500 gpm if fully sprinklered. Doesn't that 
> work with your pumps?  
> 
> Duane
> 
> ----- Original Message -----
> From: Johnson, Duane (NIH/OD/ORS) [C]
> Sent: Saturday, July 19, 2014 07:51 AM Eastern Standard Time
> To: '[email protected]' 
> <[email protected]>
> Subject: Re: Segue to AHJ's from CPVC Underground
> 
> Has Annex B been adopted?  See 101.2.1? 
> 
> Duane
> 
> ----- Original Message -----
> From: [email protected] [mailto:[email protected]]
> Sent: Saturday, July 19, 2014 07:35 AM Eastern Standard Time
> To: [email protected] 
> <[email protected]>
> Subject: Re: Segue to AHJ's from CPVC Underground
> 
> Hi John,
> What Ron didn't say is that the AHJ is trying to connect chapter 5 of the IFC 
> and table B105.2 fire flow requirements to our sprinkler system pumps. We 
> conceded early on to furnish a redundant pump because it was specified that 
> way, but the FM is expecting the fire pumps to provide the 4000 GPM from 
> B105.2 at the sprinkler (ESFR) demand pressure (165 PSI) and do so at the 
> 100% design point of the fire pump. We submitted our design with two 1500 GPM 
> pumps piped in parallel along with calcs for the storage sprinklers flowing 
> at around 165 PSI at the pump discharge. The city water system which supplies 
> the project flow tested at 5700 GPM at 74 PSI from two 4" hydrant butts. No 
> one at the AHJ's office understands how to read a fire code, or any other 
> code for that matter. They are "Code Alchemist", taking a paragraph from 
> chapter 5,  table from the annex, and numbers from our calcs, mix 'em all 
> together in an AHJ beaker and BOOM!! "Minimum code requirement". See? This 
> stuff ain
 't
>  all that hard.
> 
> Mark at Aero
> 602 820-7894
> 
> Sent from my iPad
> 
> On Jul 19, 2014, at 2:24 AM, "John Drucker" 
> <[email protected]<mailto:[email protected]>> wrote:
> 
> Like how you wrote; " everything is per code except we have".  "Except" ?, 
> Are you/they saying that having two pumps rather than one is a violation; 
> I.e. " 4000 GPM at 160 vs 4000 at 165" and you're short 5 psi ?  So two code 
> violations, two pumps and short 5 psi. Now before you chop my head off, 
> consider two things wheres the one pump and 165 psi coming from ? Somehow 
> apparently this has been planted in the ahjs head, I'm certain he/she didn't 
> come up with it on there own. Now you're stuck.  Frankly and using common 
> sense are you hitting demand, does everything fit and work together, is the 
> principal designer and owner ok with it ?  Move forward.
> 
> John Drucker - Mobile Email
> [email protected]<mailto:[email protected]><mailto:[email protected]>
> Cell/Text 732-904-6823
> 
> 
> [email protected]<mailto:[email protected]> wrote:
> 
> How about everything is per code except we have two pumps rather than one.and 
> we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most ignorant 
> thing I have ever seen. Just found out the chief told plan reviewer no more 
> written correspondence. I guess because they don't want a written orecord of 
> their stupidity. Please forgive my frustration but I just don't know where to 
> go from here..
> 
> Ron fletcher Sent from my iPhone
> 
> On Jul 18, 2014, at 4:24 PM, "John Drucker - Home" 
> <[email protected]<mailto:[email protected]>> wrote:
> 
> Ron, et.al.
> 
> I don't know the particulars of your situation but we have a saying; there's
> your side, their side and the truth.  Perhaps there's an issue with the code
> itself,  a local amendment or interpretation. There's got to be something
> driving this.
> 
> Case in point about a reference standard, NFPA-72 speaks of wall mounted
> smoke detectors/alarms and calls out a distance yet the illustration in the
> annex is worded differently than the code.
> 
> 29.8.3.3 Wall Mounting. Smoke alarms or smoke detectors mounted on walls
> shall be located NOT FARTHER than 12 in. (300 mm) from the adjoining ceiling
> surface.
> 
> Yet the annex A.29.8.3 notes;  "Measurements shown are to the closest edge
> of the detector".
> 
> According to the annex this would place part or most of the alarm or
> detector FARTHER than 12 in. from the adjoining ceiling surface.
> 
> It's important to note that Annex A opens with the following statement;
> 
> "Annex A is not a part of the requirements of this NFPA document but is
> included for informational purposes only. This annex contains explanatory
> material, numbered to correspond with the applicable text paragraphs"
> 
> Yet when brought to NFPA's attention the answer from the NFPA representative
> was interpreted from the Annex material.  This is clearly incorrect, the
> annex and the illustration are not part of the code.  In either case fix the
> code language or the annex.   The same happens in I Code Commentaries and
> various subject matter books that often interpret, amend or supplement the
> actual code language.  In a nutshell our codes and standards have become a
> maze of requirements, exceptions and interpretations.  This should be a
> warning flag to the code community.  Perhaps the code official has just
> reached his limit and is instead relying on empirical experience in the face
> of confusion.
> 
> I have situation at this very moment on two different projects that impose
> an operational issue for the fire department, one that the code is not
> considering.  However my approach is to get everyone around the table do
> some brainstorming and come up with an equitable technical solution.
> Perhaps by finding the root cause of your situation the stakeholders will
> put down their swords and solve the problem.   Food for thought.
> 
> Best wishes, always available should the need arise.
> 
> Sincerely,
> 
> John
> 
> John Drucker, CET
> Assistant Construction Official
> Fire Protection Subcode Official
> Building/Fire/Electrical Inspector
> Borough of Red Bank
> Red Bank, New Jersey
> Email: [email protected]<mailto:[email protected]>
> Cell/Text: 732-904-6823
> 
> Safe Buildings Save Lives !
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of [email protected]<mailto:[email protected]>
> Sent: Friday, July 18, 2014 1:04 PM
> To: 
> [email protected]<mailto:[email protected]>
> Subject: Segue to AHJ's from CPVC Underground
> 
> It's Friday so I figured I'd whine on the forum.  To set the stage, prior to
> the letter I am referring to we had approved permitted drawings from the
> AHJ. The following is a quote from a letter we received from that same AHJ.
> 
> "At this time , Blah Blah Blah Fire Protection District is denying said
> plans and is requesting a re-submittal of new plans that exceed IFC, UFC,
> and NFPA standards." Nowhere in the body of the letter does he say exactly
> how we are to "EXCEED" IFC, UFC and NFPA. In the letter they basically
> outline that what was submitted meets the all of the codes. I was told by
> the author of the letter at a meeting the day before that he didn't care
> what the code said because he is the AHJ and per Section 104 of the IFC he
> can make us do whatever he wants. Then he said "do it my way or there will
> be no Certificate of Occupancy."  We are 4-5 weeks away from a CofO and the
> change involves increasing the size of two new diesel pumps that are being
> installed. The fire chief told us to go to the State Fire Marshal if we
> wanted to appeal. I'm a bit frustrated with AHJ's right now.
> 
> Ron F
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]<mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]<mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]<mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]<mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to