Ron,  The only way its going to get on the record legally and be adjudicated. 

Best Wishes

John

________________________________________
From: Sprinklerforum [[email protected]] on behalf 
of [email protected] [[email protected]]
Sent: Sunday, July 20, 2014 8:24 PM
To: [email protected]
Subject: Re: Segue to AHJ's from CPVC Underground

I am filing an appeal, for all the good it will do. Have to get CofO then I can 
fight the the good but futile fight.

Ron fletcher Sent from my iPhone

> On Jul 20, 2014, at 5:10 PM, "John Drucker - Home" <[email protected]> 
> wrote:
>
> Actually you get a notice of violation, order to pay penalty, order to
> vacate and the building posted at each entrance. Disregarding the order may
> be chargeable as defiant trespass of a lawful order (which it is because the
> fact is you don't have a CO to occupy) which becomes a criminal matter, the
> hole is getting deeper.  Keep in mind the CO notice of violation, penalty
> and vacate orders are a slam dunk for the code official since the first
> question at the hearing is; "do you have a Certificate of Occupancy ?",
> which is the matter at hand. Of course the only answer other than lying is
> No.  The next question will be "did you appeal the code officials
> determination on the fire pump ?" again the answer, other than lying is No
> to which the judge or board says; "why not ?" The appeal on the fire pump
> can't even be heard because there is no appeal since the aggrieved party
> never filed one. Typically judges or boards cant order a CO issued in
> violation of the regulations which require all inspections to be completed
> and signed off, especially for fire.  Of course cooler heads will prevail
> and the directive will be to get everyone to solve the problem which is
> where we started.
>
> Besides all that we get requests from financial institutions, insurance
> companies and other vested interests every day for proof of certificate of
> occupancy prior to occupancy.
>
> Guys either get everyone together and solve it or FILE THE APPEAL it's not
> going to go away.  Let me off this ride I'm getting dizzy.
>
> PS as for the public, the angst will turn against the person(s) who occupied
> without a CO not the code official simply by virtue that the public's
> response will be " I had to get permits, inspections and a CO before
> occupancy why don't they, who do they think they are , special ?"
>
> PSS, we agree to disagree but were still friends.
>
> John
>
> John Drucker, CET
> Assistant Construction Official
> Fire Protection Subcode Official
> Building/Fire/Electrical Inspector
> Borough of Red Bank
> Red Bank, New Jersey
>
>
>
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Cahill, Christopher
> Sent: Sunday, July 20, 2014 7:06 PM
> To: [email protected]
> Subject: RE: Segue to AHJ's from CPVC Underground
>
> Theoretically at best "If an owner occupies without the COO, he/ she is
> subject to arrest by armed marshals."  Reality is you get a ticket for an
> ordinance violation.  About the same as a ticket for your long grass.
> Getting a ticket is a GOOD thing if you are right. You get to a judge to put
> the executive branch in their place. If you wait for the obstinate official
> to issue a COO you may never get use of your building or in front of a
> judge.
>
> Chris
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Forest Wilson
> Sent: Saturday, July 19, 2014 6:06 PM
> To: [email protected]
> Subject: Re: Segue to AHJ's from CPVC Underground
>
> The COO is more than just a formality.
> If an owner occupies without the COO, he/ she is subject to arrest by armed
> marshals.
> It doesnt matter if its a mall owner or a small homeowner out in the middle
> of nowhere.
> If she/he resists arrest or removal they may be killed, and at the very
> minimum imprisoned.
> Why would any sensible owner risk that over a piece of paper?
>
> A friend of mine is a roofing contractor.
> They had a regional contract with a fast food chain; one of the projects was
> in the greater Chicago area. They needed a sign off but the AHJ would not
> schedule the inspection. Finally he went down to her office and she told
> him: WE dont like you here (he was non union) and dont want you here.
> He agreed to never do business in her jurisdiction again; in return she went
> out and signed off on the roof inspection.
>
> Since you are the out of town contractor, have you considered that perhaps
> the AHJ is sending you a similar message of staying out of town and not
> biting into the locals work?
>
>
>> On 7/19/2014 6:54 PM, John Drucker - Home wrote:
>> Bob,
>>
>> Unfortunately they can indirectly by withholding a certificate of
>> approval, compliance or occupancy.  Most property owners need this
>> document for closing, insurance or tenancy and or their attorney
>> advises them that they will or have now broken an adopted law or
>> regulation.  So despite the illegitimacy of the code officials claim
>> the property owner or tenant has now legitimately broken the rules by
>> occupying without a certificate of occupancy and or certificate of
>> approval. In other words the enforcing agency holds the cards.
>>
>> Code Enforcement is a legal process and like all or most legal
>> processes in the United States the aggrieved must petition for relief,
>> in code enforcement parlance by filing an appeal.  The appeal allows
>> the appellant to present his/her position to an independent body who
>> will render a decision in favor of the appellant or the government.  I
>> cant speak for other states but in New Jersey decisions of boards of
>> appeals are binding on the enforcing agency, but this is important
>> they don't set precedent and or amend the code. In other words one
>> could win an appeal in one jurisdiction only to have to go through the
>> process in another.  As for the state level unless theirs maleficence
>> the state cannot overrule a local enforcing agency since the local
>> enforcing agencies appointment bestows approval authority to the local
> enforcing agency.
>>
>> There is good reason for this, to avoid undue political influence,
>> approve this project but not this one.  So what's a contractor to do,
>> file an appeal, that's the proper route, but keep in mind that boards
>> of appeal typically set aside cost of compliance issues much like
>> requests for variations cannot be based on financial hardship. So be
>> sure the code official is imposing above and beyond the adopted code
> including any
>> interpretive authority bestowed to the code official.   Those in the
>> electrical field know all too well about NEC;
>>
>> NEC 90.4 Enforcement. This Code is intended to be suitable for
>> mandatory application by governmental bodies that exercise legal
>> jurisdiction over electrical installations, including signaling and
>> communications systems, and for use by insurance inspectors. The
>> authority having jurisdiction for enforcement of the Code has the
>> responsibility for making interpretations of the rules, for deciding
>> on the approval of equipment and materials, and for granting the
>> special permission contemplated in a number of the rules. By special
>> permission, the authority having jurisdiction may waive specific
>> requirements in this Code or permit alternative methods where it is
>> assured that equivalent objectives can be achieved by establishing and
>> maintaining effective safety. This Code may require new products,
>> constructions, or materials that may not yet be available at the time
>> the Code is adopted. In such event, the authority having jurisdiction
>> may permit the use of the products, constructions, or materials that
> comply with the most recent previous edition of this Code adopted by the
> jurisdiction.
>>
>> So there you have it in a nutshell, I'm not siding with either party
>> just presenting information.  Best wishes.
>>
>> Sincerely,
>>
>> John Drucker, CET
>> Assistant Construction Official
>> Fire Protection Subcode Official
>> Building/Fire/Electrical Inspector
>> Borough of Red Bank
>> Red Bank, New Jersey
>> Email: [email protected]
>> Cell/Text: 732-904-6823
>>
>>
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]]
>> On Behalf Of Bob
>> Sent: Saturday, July 19, 2014 2:49 PM
>> To: [email protected]
>> Subject: RE: Segue to AHJ's from CPVC Underground
>>
>> What does unwritten policy have to do with anything?  If it's not an
>> adopted code amendment can they enforce it legally?
>>
>> Thank You,
>>
>> Bob Knight, CET III
>> 208-318-3057
>> www.Firebyknight.com
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]]
>> On Behalf Of [email protected]
>> Sent: Saturday, July 19, 2014 6:15 AM
>> To: [email protected]
>> Subject: Re: Segue to AHJ's from CPVC Underground
>>
>> The stance of the AHJ is that their unwritten policy is pumps can only
>> be used at 100%. They also believe that 1500 gpm pumps will only
>> produce 1500 gpm, and we have to use 2 2000 gpm pumps to get 4000 gpm.
>> They don't think pressure is even a factor.
>>
>> Ron fletcher Sent from my iPhone
>>
>>>> On Jul 19, 2014, at 5:00 AM, "Johnson, Duane (NIH/OD/ORS) [C]"
>>> <[email protected]> wrote:
>>> There are so many things wrong here. But, you may be able to make
>>> this
>> work regardless. Did you take your 75% reduction in fire flow based on
>> the fully sprinklered exception in B105.2? If you are starting at 4000
>> gpm, the required flow can be reduced to 1500 gpm if fully
>> sprinklered. Doesn't that work with your pumps?
>>> Duane
>>>
>>> ----- Original Message -----
>>> From: Johnson, Duane (NIH/OD/ORS) [C]
>>> Sent: Saturday, July 19, 2014 07:51 AM Eastern Standard Time
>>> To: '[email protected]'
>>> <[email protected]>
>>> Subject: Re: Segue to AHJ's from CPVC Underground
>>>
>>> Has Annex B been adopted?  See 101.2.1?
>>>
>>> Duane
>>>
>>> ----- Original Message -----
>>> From: [email protected] [mailto:[email protected]]
>>> Sent: Saturday, July 19, 2014 07:35 AM Eastern Standard Time
>>> To: [email protected]
>>> <[email protected]>
>>> Subject: Re: Segue to AHJ's from CPVC Underground
>>>
>>> Hi John,
>>> What Ron didn't say is that the AHJ is trying to connect chapter 5 of
>>> the IFC and table B105.2 fire flow requirements to our sprinkler
>>> system pumps. We conceded early on to furnish a redundant pump
>>> because it was specified that way, but the FM is expecting the fire
>>> pumps to provide the 4000 GPM from B105.2 at the sprinkler (ESFR)
>>> demand pressure (165 PSI) and do so at the 100% design point of the
>>> fire pump. We submitted our design with two 1500 GPM pumps piped in
>>> parallel along with calcs for the storage sprinklers flowing at
>>> around
>>> 165 PSI at the pump discharge. The city water system which supplies
>>> the project flow tested at 5700 GPM at 74 PSI from two 4" hydrant
>>> butts. No one at the AHJ's office understands how to read a fire
>>> code, or any other code for that matter. They are "Code Alchemist",
>>> taking a paragraph from chapter 5,  table from the annex, and numbers
>>> from our calcs, mix 'em all together in an AHJ beaker and BOOM!!
>>> "Minimum code requirement". See? This stuff ain
>>  't
>>>  all that hard.
>>>
>>> Mark at Aero
>>> 602 820-7894
>>>
>>> Sent from my iPad
>>>
>>>> On Jul 19, 2014, at 2:24 AM, "John Drucker"
>>> <[email protected]<mailto:[email protected]>> wrote:
>>> Like how you wrote; " everything is per code except we have".
>>> "Except" ?,
>> Are you/they saying that having two pumps rather than one is a
>> violation; I.e. " 4000 GPM at 160 vs 4000 at 165" and you're short 5
>> psi ?  So two code violations, two pumps and short 5 psi. Now before
>> you chop my head off, consider two things wheres the one pump and 165
>> psi coming from ? Somehow apparently this has been planted in the ahjs
>> head, I'm certain he/she didn't come up with it on there own. Now
>> you're stuck.  Frankly and using common sense are you hitting demand,
>> does everything fit and work together, is the principal designer and owner
> ok with it ?  Move forward.
>>> John Drucker - Mobile Email
>>> [email protected]<mailto:[email protected]><mailto:jdrucker
>>> @
>>> redbanknj.org>
>>> Cell/Text 732-904-6823
>>>
>>>
>>> [email protected]<mailto:[email protected]> wrote:
>>>
>>> How about everything is per code except we have two pumps rather than
>> one.and we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi.
>> Most ignorant thing I have ever seen. Just found out the chief told
>> plan reviewer no more written correspondence. I guess because they
>> don't want a written orecord of their stupidity. Please forgive my
>> frustration but I just don't know where to go from here..
>>> Ron fletcher Sent from my iPhone
>>>
>>>> On Jul 18, 2014, at 4:24 PM, "John Drucker - Home"
>>> <[email protected]<mailto:[email protected]>> wrote:
>>> Ron, et.al.
>>>
>>> I don't know the particulars of your situation but we have a saying;
>>> there's your side, their side and the truth.  Perhaps there's an
>>> issue with the code itself,  a local amendment or interpretation.
>>> There's got to be something driving this.
>>>
>>> Case in point about a reference standard, NFPA-72 speaks of wall
>>> mounted smoke detectors/alarms and calls out a distance yet the
>>> illustration in the annex is worded differently than the code.
>>>
>>> 29.8.3.3 Wall Mounting. Smoke alarms or smoke detectors mounted on
>>> walls shall be located NOT FARTHER than 12 in. (300 mm) from the
>>> adjoining ceiling surface.
>>>
>>> Yet the annex A.29.8.3 notes;  "Measurements shown are to the closest
>>> edge of the detector".
>>>
>>> According to the annex this would place part or most of the alarm or
>>> detector FARTHER than 12 in. from the adjoining ceiling surface.
>>>
>>> It's important to note that Annex A opens with the following
>>> statement;
>>>
>>> "Annex A is not a part of the requirements of this NFPA document but
>>> is included for informational purposes only. This annex contains
>>> explanatory material, numbered to correspond with the applicable text
>> paragraphs"
>>> Yet when brought to NFPA's attention the answer from the NFPA
>>> representative was interpreted from the Annex material.  This is
>>> clearly incorrect, the annex and the illustration are not part of the
>> code.  In either case fix the
>>> code language or the annex.   The same happens in I Code Commentaries and
>>> various subject matter books that often interpret, amend or
>>> supplement the actual code language.  In a nutshell our codes and
>>> standards have become a maze of requirements, exceptions and
>>> interpretations.  This should be a warning flag to the code
>>> community.  Perhaps the code official has just reached his limit and
>>> is instead relying on empirical experience in the face of confusion.
>>>
>>> I have situation at this very moment on two different projects that
>>> impose an operational issue for the fire department, one that the
>>> code is not considering.  However my approach is to get everyone
>>> around the table do some brainstorming and come up with an equitable
>>> technical
>> solution.
>>> Perhaps by finding the root cause of your situation the stakeholders will
>>> put down their swords and solve the problem.   Food for thought.
>>>
>>> Best wishes, always available should the need arise.
>>>
>>> Sincerely,
>>>
>>> John
>>>
>>> John Drucker, CET
>>> Assistant Construction Official
>>> Fire Protection Subcode Official
>>> Building/Fire/Electrical Inspector
>>> Borough of Red Bank
>>> Red Bank, New Jersey
>>> Email: [email protected]<mailto:[email protected]>
>>> Cell/Text: 732-904-6823
>>>
>>> Safe Buildings Save Lives !
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]]
>>> On Behalf Of [email protected]<mailto:[email protected]>
>>> Sent: Friday, July 18, 2014 1:04 PM
>>> To:
>>> [email protected]<mailto:[email protected]
>>> r
>>> esprinkler.org>
>>> Subject: Segue to AHJ's from CPVC Underground
>>>
>>> It's Friday so I figured I'd whine on the forum.  To set the stage,
>>> prior to the letter I am referring to we had approved permitted
>>> drawings from the AHJ. The following is a quote from a letter we
>>> received
>> from that same AHJ.
>>> "At this time , Blah Blah Blah Fire Protection District is denying
>>> said plans and is requesting a re-submittal of new plans that exceed
>>> IFC, UFC, and NFPA standards." Nowhere in the body of the letter does
>>> he say exactly how we are to "EXCEED" IFC, UFC and NFPA. In the
>>> letter they basically outline that what was submitted meets the all
>>> of the codes. I was told by the author of the letter at a meeting the
>>> day before that he didn't care what the code said because he is the
>>> AHJ and per Section 104 of the IFC he can make us do whatever he wants.
>>> Then he said "do it my way or there will be no Certificate of
>>> Occupancy."  We are 4-5 weeks away from a CofO and the change
>>> involves increasing the size of two new diesel pumps that are being
> installed.
>>> The fire chief told us to go to the State Fire Marshal if we wanted
>>> to
>> appeal. I'm a bit frustrated with AHJ's right now.
>>> Ron F
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]<mailto:[email protected]
>>> r
>>> esprinkler.org>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l
>>> er.org
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]<mailto:[email protected]
>>> r
>>> esprinkler.org>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l er.org _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]<mailto:[email protected]
>>> r
>>> esprinkler.org>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l er.org _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]<mailto:[email protected]
>>> r
>>> esprinkler.org>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l er.org _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l er.org _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l
>>> er.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>
>
> --
> Forest Wilson
> Project Manager
> 193 California St
> Xenia OH 45385
> Ph: 937-736-0425
>
> ///WHO IS JOHN GALT?///
>
> ******This email and any files transmitted with it are confidential and
> intended solely for the use of the individual or entity to whom they are
> addressed. If you have received this email in error please notify the system
> manager. This message contains confidential information and is intended only
> for the individual named. If you are not the named addressee you should not
> disseminate, distribute or copy this e-mail. Please notify the sender
> immediately by e-mail if you have received this e-mail by mistake and delete
> this e-mail from your system. If you are not the intended recipient you are
> notified that disclosing, copying, distributing or taking any action in
> reliance on the contents of this information is strictly prohibited.***
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to