What is the nature of the building construction? I have seen buildings over 4 stories use 13R because the lower stories were separated with a horizontal barrier that allowed the upper 4 stories of residential occupancy to be classified as its own building.
Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Monday, July 28, 2014 10:40 AM To: [email protected] Subject: 6 Story Hotel Having a little debate here in the office..... Looking at a 6 story hotel and (1) person wants to use NFPA-13R & (1) says you can't because it's over 4 stories and you must use NFPA-13. Comments welcome .... :) Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org