Not sure what you need but the IBC has requirements for foam insulated cooler 
walls.  From the 2006 edition.

2603.4.1.2 Cooler and freezer walls. Foam plastic
installed in a maximum thickness of 10 inches (254 mm)
in cooler and freezer walls shall:
1. Have a flame spread index of 25 or less and a
smoke-developed index of not more than 450,
where tested in a minimum 4 inch (102 mm) thickness.
2. Have flash ignition and self-ignition temperatures
of not less than 600°F and 800°F (316°C and
427°C), respectively.
3. Have a covering of not less than 0.032-inch (0.8
mm) aluminum or corrosion-resistant steel having
a base metal thickness not less than 0.0160 inch
(0.4 mm) at any point.
4. Be protected by an automatic sprinkler system.
Where the cooler or freezer is within a building,
both the cooler or freezer and that part of the building
in which it is located shall be sprinklered.

John Hoffman, PE
Facility Engineering Services KCP, LLC -- Burns & McDonnell Engineering
National Nuclear Security Administration's KC Plant
Operated by Honeywell FM&T, LLC
office: 816-488-7213
[email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Martinez, Dewayne
Sent: Friday, August 01, 2014 10:02 AM
To: [email protected]
Subject: cooler panel walls

Anyone know if the metal insulated panel walls used in coolers /
freezers are considered combustible?    

Thanks,

Dewayne 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to