You need to very which insulation is inside. FM had requirements of face
sprinklers tightly spaced, no more than 2'-0" from the wall. I have heard
descriptions of flowing, burning gasoline when dealing with these.
On Aug 1, 2014 2:22 PM, "John Hoffman" <[email protected]> wrote:

> I don't think you can consider these panels "limited combustible".  I
> recall a fire in Boston a few years ago involving a warehouse building full
> of coolers.  I believe some firefighters did not make it out.   The foam
> in-between the panels will melt in a fire and pool into a flammable liquid
> fire.
>
> John Hoffman, PE
> Facility Engineering Services KCP, LLC -- Burns & McDonnell Engineering
> National Nuclear Security Administration's KC Plant
> Operated by Honeywell FM&T, LLC
> office: 816-488-7213
> [email protected]
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Martinez,
> Dewayne
> Sent: Friday, August 01, 2014 10:43 AM
> To: [email protected]
> Subject: RE: cooler panel walls
>
> Thanks,
> The GC wanted to extend the cooler walls to the deck above and I needed to
> know if the concealed space between the top of the cooler and the deck
> needed sprinkler protection.  Statement 4 would dictate that we would need
> sprinkler protection but the walls appear to meet the definition of limited
> combustible which per NFPA 13 would not require sprinkler
> protection......clear as mud
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of John Hoffman
> Sent: Friday, August 01, 2014 10:26 AM
> To: [email protected]
> Subject: RE: cooler panel walls
>
> Not sure what you need but the IBC has requirements for foam insulated
> cooler walls.  From the 2006 edition.
>
> 2603.4.1.2 Cooler and freezer walls. Foam plastic installed in a maximum
> thickness of 10 inches (254 mm) in cooler and freezer walls shall:
> 1. Have a flame spread index of 25 or less and a smoke-developed index of
> not more than 450, where tested in a minimum 4 inch (102 mm) thickness.
> 2. Have flash ignition and self-ignition temperatures of not less than
> 600°F and 800°F (316°C and 427°C), respectively.
> 3. Have a covering of not less than 0.032-inch (0.8
> mm) aluminum or corrosion-resistant steel having a base metal thickness
> not less than 0.0160 inch
> (0.4 mm) at any point.
> 4. Be protected by an automatic sprinkler system.
> Where the cooler or freezer is within a building, both the cooler or
> freezer and that part of the building in which it is located shall be
> sprinklered.
>
> John Hoffman, PE
> Facility Engineering Services KCP, LLC -- Burns & McDonnell Engineering
> National Nuclear Security Administration's KC Plant Operated by Honeywell
> FM&T, LLC
> office: 816-488-7213
> [email protected]
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Martinez,
> Dewayne
> Sent: Friday, August 01, 2014 10:02 AM
> To: [email protected]
> Subject: cooler panel walls
>
> Anyone know if the metal insulated panel walls used in coolers /
> freezers are considered combustible?
>
> Thanks,
>
> Dewayne
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to