Thanks Roland.  I came to a similar conclusion yesterday figuring that as
long as the sprinkler is in the transverse flue and positioned with respect
to the longitudinal flue that where it landed wasn't as important as not
exceeding the max 10' vertical spacing.  This helps to solidify my
conclusion.

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Thursday, August 21, 2014 10:05 AM
To: [email protected]
Subject: Re: In-Rack Sprinklers

Although not well emphasized and inconsistently stated Vertical placement is
APPROXIMATE and horizontal is a maximum. Look at the sub-titles of Table
16.3.1.1

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Aug 20, 2014, at 11:26 AM, Bob <[email protected]> wrote:

> Let me rephrase my question, where would the intersection of the 
> transverse flue and longitudinal flue be?  Is it literally between 
> loads as the figures in 13 show, or can the intersection be anywhere 
> along the height of the load up to the maximum of 10'?
> 
> Thank You,
> 
> Bob Knight, CET III