Thanks Roland. I came to a similar conclusion yesterday figuring that as long as the sprinkler is in the transverse flue and positioned with respect to the longitudinal flue that where it landed wasn't as important as not exceeding the max 10' vertical spacing. This helps to solidify my conclusion.
Thank You, Bob Knight, CET III 208-318-3057 www.Firebyknight.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Thursday, August 21, 2014 10:05 AM To: [email protected] Subject: Re: In-Rack Sprinklers Although not well emphasized and inconsistently stated Vertical placement is APPROXIMATE and horizontal is a maximum. Look at the sub-titles of Table 16.3.1.1 Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Aug 20, 2014, at 11:26 AM, Bob <[email protected]> wrote: > Let me rephrase my question, where would the intersection of the > transverse flue and longitudinal flue be? Is it literally between > loads as the figures in 13 show, or can the intersection be anywhere > along the height of the load up to the maximum of 10'? > > Thank You, > > Bob Knight, CET III _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org