Check the structural notes. If it is seismic design category a or b, then no 
seismic. If SDC of C or higher then bracing required. 

It seems odd to do seismic bracing of piping if the building is not designed to 
resist seismic forces. 

Travis Mack, SET
MFP Design, LLC

Sent from my iPhone

> On Sep 5, 2014, at 5:32 AM, <[email protected]> wrote:
> 
> The AHJ can't just "require it".  His preference is not relevant.  Also 
> seismic bracing is not based on Zones or Maps anymore, hasn't been for quite 
> a while. 
> 
> I'm curious why you're using the 2000 edition of NFPA 13.
> 
> Anyway back to seismic.
> 
> Seismic requirements are determined based on a number of factors originating 
> out of the Building Code Chapter 16.  It's not just an arbitrary decision.   
> 
> There needs to be a geotech (soils) report, the building needs to be 
> classified as to its use/function and you go from there.
> 
> So there are engineering questions to be answered before there a requirement 
> for bracing is established.
> 
> I've had to provide bracing on new work in an existing building, it made no 
> sense since the building structure wasn't design for the loading and the rest 
> of the system was not protected but it was required by the code so it had to 
> be done.  Was it required on the original install, did someone just miss it 
> assuming the site wasn't in "the zone", who knows.
> 
> There is a lot of misinterpretation on the part of design professionals 
> regard when it's required and when it's not.
> 
> Craig L. Prahl 
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Steve Sorrell
> Sent: Friday, September 05, 2014 8:13 AM
> To: [email protected]
> Subject: Seismic bracing
> 
> I need some help with a seismic problem.
> I am making modifications to a 1970's sprinkler system in NC, we are using 
> the 2000 ed of NFPA  13.
> There is no seismic bracing on this system.
> I have had to add some new main in various areas.
> The local AHJ is requiring that only the new sprinkler main will need to be 
> braced.
> Does anyone know if this is an actual standards requirement or just a 
> preference of the local AHJ ?
> Obviously I am trying to avoid installing the seismic bracing on this project.
> 
> 
> Stephen J. Sorrell, CET
> NICET# 77901 Level III
> E mail: [email protected]<mailto:[email protected]>
> 
> Performance Fire Protection, LLC
> Corporate Office
> 179 Gasoline Alley -  PO Box 4510
> Mooresville, NC 28117
> Phone: 704-663-1664  Fax: 704-663-1652
> Cell : 704-309-1242
> 
> Web: www.performancefire.com<http://www.performancefire.com>
> Licensed in NC, SC, VA, TN, GA, AL
> 
> "Performance on Every Level."
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to