So purely along the lines of Andy Rooney's 'have you ever wondered why' :)
... FM Datasheet 2-0, while not limiting the allowable velocity, does
require that when velocity exceed 30ft/sec, that the calculation be
performed via the Darcy-Weisbach Method rather than the Hazen-Williams.
Entertainment value only, but would seem that the variance between results
in Hazen-Williams versus Darcy-Weisbach become more apparent with higher
velocities.
The 30ft/sec limitation (for application of Hazen-Williams calculations) in
FM 2-0 is strangely close to the 10m/sec (32.8ft/sec) limitation in EN
12845 Rules for Automatic Sprinkler Installations (previously BS 5306).




On 15 September 2014 21:23, Parsley Consulting <[email protected]>
wrote:

> Roland,
>     A mutual friend of ours who works up in Quincy described for me a
> question he once had with a caller who wanted to know in which edition of
> -13 the 32 ft/sec requirement had been removed, and why.
>     This friend searched through the library there back to the first
> sprinkler standard from 1896, and found that it had NEVER been part of
> -13.  The individual he was dealing with accused him of being an imbecile
> and a deceitful one to boot, and promptly hung up.
>     Joe Hankins told me the same story.
> *Ken Wagoner, SET
> *Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, California 92025
> *****Phone 760-745-6181*
> Visit our website <http://www.parsleyconsulting.com/> ***
> On 9/15/2014 1:01 PM, Roland Huggins wrote:
>
>> Next time you even start to think of any basis for imposing a velocity of
>> 32 ft/s, take a hammer and smash a finger.  Hopefully the pain will divert
>> you from wasting your time especially if you’re assuming you are dealing
>> with facts.  I’ve heard numerous conclusion as to why the mystical 32 ft/s
>> existed.  Only one has any chance of being valid.  Joe Hankins told me long
>> ago that FM initially imposed a velocity restriction after hydraulic calc’s
>> entered the scene and folks started designing gridded storage systems with
>> 1 inch BLs.  For ever other basis, I can hear Andy Rooney saying - Have you
>> ever wondered why …...
>>
>> Roland
>>
>>
>> Roland Huggins, PE - VP Engineering
>> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
>> Dallas, TX
>> http://www.firesprinkler.org
>>
>>
>>
>>
>>
>> On Sep 12, 2014, at 5:51 AM, Brad Casterline <[email protected]>
>> wrote:
>>
>>  Damien, will you mail me those snaps too please? I have heard the pipe
>>> schedules were derived by increasing the size when the velocity reached
>>> about 32 ft/sec. Figuring out approximate flow per head and average
>>> densities, etc, will give me something to do as I sit at the kitchen
>>> table
>>> and drink beer tonight. Thanks.
>>>
>>> Good luck Jeremy!
>>>
>>> Brad
>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
>> org
>>
>>
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>



-- 

*Damien Shannon*
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to