Roland,

Did Joe tell you on what basis the Technical Committees accepted the Pipe
Schedules?

Here is an excerpt from the follow-up post to the you one you posted (EC
stands for European Code, and I was going to say British Standard, call it
BS, but thought better):

"For the EC schedule with max 4 head line, using 32 ft/sec as the cut-off
and 130 ft2 spacing I got an average density of 0.192 GPM/ft2. For the NFPA
schedule, using 20 ft/sec as the cut-off and 130 ft2 spacing I got an
average density of 0.200 GPM/ft2."

So having done that it seemed reasonable to flow about 26 GPM/head based on
not knowing the water supply, as something to shoot for anyway. Until
someone suggests something more reasonable I will go with it, not that it
matters in today's world, I am just always wondering why ....

Brad

-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Monday, September 15, 2014 3:13 PM
To: [email protected]
Subject: RE: Water Velocity

Hilarious Roland. Will do, now that I am done coming up with not only 32
ft/sec, but 20 ft/sec too! And the beer was good (while it lasted).

Here is the one I like-- it kills the 7 PSI and the 32 ft/sec birds with one
stone:

7/.433=16.166 ft (h). v=SQRT(2gh) = (2*32.2*16.166)^.5= 32.27 ft/sec

:)

Thanks for the attention sir!

Brad


-----Original Message-----
From: Roland Huggins [mailto:[email protected]] 
Sent: Monday, September 15, 2014 3:02 PM
To: [email protected]
Subject: Water Velocity

Next time you even start to think of any basis for imposing a velocity of 32
ft/s, take a hammer and smash a finger.  Hopefully the pain will divert you
from wasting your time especially if you're assuming you are dealing with
facts.  I've heard numerous conclusion as to why the mystical 32 ft/s
existed.  Only one has any chance of being valid.  Joe Hankins told me long
ago that FM initially imposed a velocity restriction after hydraulic calc's
entered the scene and folks started designing gridded storage systems with 1
inch BLs.  For ever other basis, I can hear Andy Rooney saying - Have you
ever wondered why ....

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Sep 12, 2014, at 5:51 AM, Brad Casterline <[email protected]>
wrote:

> Damien, will you mail me those snaps too please? I have heard the pipe
> schedules were derived by increasing the size when the velocity reached
> about 32 ft/sec. Figuring out approximate flow per head and average
> densities, etc, will give me something to do as I sit at the kitchen table
> and drink beer tonight. Thanks.
> 
> Good luck Jeremy!
> 
> Brad   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to