IBC (2006) addresses water supply valves...

903.3.5 Water supplies. 
Water supplies for automatic sprinkler systems shall comply with this section 
and the standards referenced in Section 903.3.1. The potable water supply shall 
be protected against backflow in accordance with the requirements of this 
section and the International Plumbing Code. [F]

903.4 Sprinkler system monitoring and alarms. [F]
All valves controlling the water supply for automatic sprinkler systems, pumps, 
tanks, water levels and temperatures, critical air pressures and water-flow 
switches on all sprinkler systems shall be electrically supervised. 
Exceptions: 
1.   Automatic sprinkler systems protecting one- and two-family dwellings.
2.   Limited area systems serving fewer than 20 sprinklers.
3.   Automatic sprinkler systems installed in accordance with NFPA 13R where a 
common supply main is used to supply both domestic water and the automatic 
sprinkler systems and a separate shutoff valve for the automatic sprinkler 
system is not provided.
4.   Jockey pump control valves that are sealed or locked in the open position.
5.   Control valves to commercial kitchen hoods, paint spray booths or dip 
tanks that are sealed or locked in the open position.
6.   Valves controlling the fuel supply to fire pump engines that are sealed or 
locked in the open position.
7.   Trim valves to pressure switches in dry, preaction and deluge sprinkler 
systems that are sealed or locked in the open position.

903.4.1 Signals. [F]
Alarm, supervisory and trouble signals shall be distinctly different and 
automatically transmitted to an approved central station, remote supervising 
station or proprietary supervising station as defined in NFPA 72 or, when 
approved by the fire code official, shall sound an audible signal at a 
constantly attended location. 
Exceptions:
1.   Underground key or hub valves in roadway boxes provided by the 
municipality or public utility are not required to be monitored.
2.   Backflow prevention device test valves located in limited area sprinkler 
system supply piping shall be locked in the open position. In occupancies 
required to be equipped with a fire alarm system, the backflow preventer valves 
shall be electrically supervised by a tamper switch installed in accordance 
with NFPA 72 and separately annunciated.

903.3.5.1 Domestic services. 
Where the domestic service provides the water supply for the automatic 
sprinkler system, the supply shall be in accordance with this section. [F]



Duane Johnson, PE
Design Manager
Strickland Fire Protection
301-474-1136 Office
301-455-0010 Cell



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Morey, Mike
Sent: Thursday, October 23, 2014 8:38 AM
To: [email protected]
Subject: PIV Tampering - IFC vs IBC vs NFPA

We've had an issue come up relating to PIV tampering.  We use a state adopted 
(Indiana) code that is based almost entirely on IBC/IFC 2006.  We've been asked 
to tamper PIVs per IBC/IFC.  Our site includes a large campus fire main loop 
and there is some discussion about whether or not all those valves require 
tampering.  My contention is that the campus fire main is a private fire 
service main and is outside the scope of IBC and the chapter 9 requirement to 
tamper all valves, IFC chapter 5 seems to be the correct code to apply and 
refers almost exclusively to NFPA 24 for private fire service mains.  NFPA 
allows locking and periodic checks rather than requiring electronic monitoring 
as IBC/IFC chapter 9 does.  Is there any succinct way to show the campus loop 
is out of the scope of IBC, or is my reasoning incorrect?

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
[email protected]<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=mailto%3amanta%40bmwc.com>
 | 
www.bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=http%3a%2f%2fwww.bmwc.com%2f>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to