Mike,
I don't know how it will end up in your part of the world, however here in California, a new installation of more than 20 sprinklers must have electric monitoring of any valve controlling that system. Similar language was in the 2006 IFC, in section 903.4, which read:

903.4 Sprinkler system monitoring and alarms. All valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels and temperatures, critical air pressures, and water-flowswitches on all sprinkler systems shall be electrically supervised.

Exceptions:

   1. Automatic sprinkler systems protecting one- and two-family dwellings.

   2. Limited area systems serving fewer than 20 sprinklers.

   3. Automatic sprinkler systems installed in accordance with NFPA 13R
   where a common supply main is used to supply both domestic water and
   the automatic sprinkler system, and a separate shutoff valve for the
   automatic sprinkler system is not provided.

   4. Jockey pump control valves that are sealed or locked in the open
   position.

   5. Control valves to commercial kitchen hoods, paint spray booths or
   dip tanks that are sealed or locked in the open position.

   6. Valves controlling the fuel supply to fire pump engines that are
   sealed or locked in the open position.

   7. Trim valves to pressure switches in dry, preaction and deluge
   sprinkler systems that are sealed or locked in the open position.

This would seem pretty definite that an electronic tamper switch is required.

Hope that is of some help.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***

On 10/23/2014 5:38 AM, Morey, Mike wrote:
We've had an issue come up relating to PIV tampering.  We use a state adopted 
(Indiana) code that is based almost entirely on IBC/IFC 2006.  We've been asked 
to tamper PIVs per IBC/IFC.  Our site includes a large campus fire main loop 
and there is some discussion about whether or not all those valves require 
tampering.  My contention is that the campus fire main is a private fire 
service main and is outside the scope of IBC and the chapter 9 requirement to 
tamper all valves, IFC chapter 5 seems to be the correct code to apply and 
refers almost exclusively to NFPA 24 for private fire service mains.  NFPA 
allows locking and periodic checks rather than requiring electronic monitoring 
as IBC/IFC chapter 9 does.  Is there any succinct way to show the campus loop 
is out of the scope of IBC, or is my reasoning incorrect?

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
[email protected]<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=mailto%3amanta%40bmwc.com>
 | 
www.bmwc.com<https://owa.bmwc.com/owa/redir.aspx?C=hEc2LsZXLUqfB3v1fAsIUDtQSkfsw9AIUxDXhx81O08DpGEK3NHRaSbWuncnZEk-mLpe2vYiBJY.&URL=http%3a%2f%2fwww.bmwc.com%2f>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to