I am looking at a calc and I wanted to make sure I am thinking about this correctly:
If there is a soffit that is over 8" that has sidewalls in it at the ceiling level - it also needs pendants under it. Then when the area/density calc is performed you have to flow the pendant and sidewall heads for that area - right? I can't think of any reason why you would not calc both sets of heads, but I have been getting some push back (primarily due to the increase in water volume). Just wanted to make sure I am on the right track. Thanks! Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org