Right Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com 860-535-2080 (ofc)
> On Oct 23, 2014, at 3:23 PM, Matt Grise <[email protected]> wrote: > > I am looking at a calc and I wanted to make sure I am thinking about this > correctly: > > > > If there is a soffit that is over 8" that has sidewalls in it at the ceiling > level - it also needs pendants under it. Then when the area/density calc is > performed you have to flow the pendant and sidewall heads for that area - > right? > > > > I can't think of any reason why you would not calc both sets of heads, but I > have been getting some push back (primarily due to the increase in water > volume). Just wanted to make sure I am on the right track. > > > > Thanks! > > > Matt Grisé PE*, LEED AP, NICET II > Sales Engineer > Alliance Fire Protection > 130 w 9th Ave. > North Kansas City, MO 64116 > > *Licensed in KS & MO > > 913.888.0647 ph > 913.888.0618 f > 913.927.0222 cell > www. AFPsprink.com > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org