Hey everyone. Galen emailed me the report. I have uploaded it to a
dropbox location. You should be able to access it here.
https://www.dropbox.com/s/7kbtf4aoqontp2b/NER-516%20-%20Water%20Curtain%20for%20Protection%20of%20Glazed%20Openings.pdf?dl=0
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
On 11/7/2014 10:49 AM, Taylor, Galen wrote:
Too bad about not permitting attachments. Links are not always possible, and
attachments typically provide instant information that links frequently do not.
The practice must have been abused in the past leading to their prohibition.
Have a great weekend everyone.
Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
[email protected]
"Ensuring Public Safety Through the Built Environment"
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of [email protected]
Sent: Friday, November 07, 2014 9:05 AM
To: [email protected]
Subject: RE: Water Curtain Heads
Hi Galen,
I believe you can post a link but not an attachment. Can someone confirm this.
Mark at Aero
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Taylor, Galen
Sent: Friday, November 07, 2014 9:57 AM
To: [email protected]
Subject: RE: Water Curtain Heads
Trying one more time to send Evaluation Report ...
Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
[email protected]
"Ensuring Public Safety Through the Built Environment"
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Taylor, Galen
Sent: Friday, November 07, 2014 8:51 AM
To: [email protected]
Subject: RE: Water Curtain Heads
The attached Evaluation Report from ICC Evaluation Service may be useful.
Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
[email protected]
"Ensuring Public Safety Through the Built Environment"
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Steve Sorrell
Sent: Friday, November 07, 2014 7:07 AM
To: [email protected]
Subject: Water Curtain Heads
When calculating the design area which would include heads for a water curtain,
are the heads on both sides of the protected windows Included in the
calculations or are you allowed to only calculate one side of the protected
glass.
Stephen J. Sorrell, CET
NICET# 77901 Level III
E mail: [email protected]<mailto:[email protected]>
Performance Fire Protection, LLC
Corporate Office
179 Gasoline Alley - PO Box 4510
Mooresville, NC 28117
Phone: 704-663-1664 Fax: 704-663-1652
Cell : 704-309-1242
Web: www.performancefire.com<http://www.performancefire.com>
Licensed in NC, SC, VA, TN, GA, AL
"Performance on Every Level."
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org