There is an FM Data Sheet which covers Dust Collectors etc.

Russell Gregory

Russell Gregory
41A Diamond Avenue,
Christchurch 8024
New Zealand 
 
e-mail [email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Reed A. Roisum, C.E.T.
Sent: Tuesday, 18 November 2014 11:46 a.m.
To: [email protected]
Subject: Baghouse Fire Suppression

Looking for some information on installing fire sprinklers in a
baghouse/dust collector.  I haven't been able to find anything in the NFPA
standards or elsewhere that gives any design criteria or sprinkler placement
requirements.  NFPA 654 just says " 10.5.2 Automatic sprinklers, where
provided, shall be installed in accordance with NFPA 13, Standard for the
Installation of Sprinkler Systems. "
NFPA 13 Chapter 22 looked promising but nothing there either.

There is an existing explosion suppression system installed in the baghouse
but that is a separate matter.

Any insight is appreciated.

Thank you.

Reed Roisum



Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |
http://www.kfiengineers.com

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to