First thing is to ask the client if they have any corporate standards regarding 
protection of baghouses.

There are also times when the manufacturer will provide internal suppression.  

If they don't, refer to FM Data Sheet 7-73 and also NFPA 654 for some guidance.

This is not a typical NFPA 13 job.  Most are protected by deluge systems with 
linear heat detection or other type of heat detection systems.  

Water drainage from the unit is an issue as the excess weight of accumulated 
water within can cause a structural collapse.  

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Reed A. Roisum, C.E.T.
Sent: Monday, November 17, 2014 5:46 PM
To: [email protected]
Subject: Baghouse Fire Suppression

Looking for some information on installing fire sprinklers in a baghouse/dust 
collector.  I haven't been able to find anything in the NFPA standards or 
elsewhere that gives any design criteria or sprinkler placement requirements.  
NFPA 654 just says " 10.5.2 Automatic sprinklers, where provided, shall be 
installed in accordance with NFPA 13, Standard for the Installation of 
Sprinkler Systems. "
NFPA 13 Chapter 22 looked promising but nothing there either.

There is an existing explosion suppression system installed in the baghouse but 
that is a separate matter.

Any insight is appreciated.

Thank you.

Reed Roisum



Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection Designer 
| Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
http://www.kfiengineers.com

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to