UFC 3-600-01 4-2.3.1 Sprinkler Density and Hose Stream Requirements. Building and structures requiring sprinkler protection must be provided with sprinkler systems that are designed using the Area/Density Method of NFPA 13, \2\ except the design density, design area, hose stream allowance and duration of supply requirements for non-storage occupancies must be in accordance with FM Global Loss Prevention Data Sheet 3-26, Fire Protection Water Demand for Non-Storage Sprinklered Properties Tables 1 through 4, including the revised Table 2 in FM Engineering Bulletin 04-12. /2/
I'll give you they say area/density and NFPA 13 11.2.3.2 says density/area but they mean the same thing. Small room falls under the next section 11.2.3.3 Room Design Method. UFC does not refernce you to 11.2.3 Water Demand Requirements - Hydraulic Calculation Methods. Which would get you density/area, room design and special areas. Chris Cahill, PE* Associate Fire Protection Engineer Burns & McDonnell Phone: 952.656.3652 Fax: 952.229.2923 [email protected] www.burnsmcd.com *Registered in: MN Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jerry Van Kolken Sent: Thursday, November 20, 2014 11:10 AM To: [email protected] Subject: RE: FM Global and the UFC Maybe I'm not sure what Greg is asking, but we use small room all the time on UFC jobs and have never been called on it. Chris could you point me to where it says you can't use small room? Jerry Van Kolken Millennium Fire Protection (760) 722-2722 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Cahill, Christopher Sent: Wednesday, November 19, 2014 8:24 AM To: [email protected] Subject: RE: FM Global and the UFC IDK about FM. UFC is clear to me, no you can't use small room - area/density only, and no the calcs are not per FM. There are 5 things you pull from FM and only these 5 things, density, design area, hose stream allowance, duration and minimum k-factor. And really these only apply to things defined as HC1-3. For example HPS would follow NFPA 13. Chris Cahill, PE* Associate Fire Protection Engineer Burns & McDonnell Phone: 952.656.3652 Fax: 952.229.2923 [email protected] www.burnsmcd.com *Registered in: MN Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Wednesday, November 19, 2014 10:17 AM To: [email protected] Subject: FM Global and the UFC Does FM allow the "small room rule" for end head pressures in small room rules as in NFPA #13? The UFC is confusing as the installation goes by 13 and the calcs go by FM standards..... Thanks, Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org