I am always surprised at how many left handed valves there are out there.  
While investigating some issues with a new fire pump Installation in Charlotte, 
we found 3 left handed valves, 1 open, 1 half closed, and 1 3/4 plus closed.  I 
really don't like these, especially on a gridded underground system because 
unless you have a very diligent inspection dept, it is way too easy to leave a 
valve closed.  In our situation, we caught the low flow due to the fire pumper 
test suction dropping to +\- 10 psi @ under 500 GPM. It ended up being a 
secondary main feeding hydrants had been inadvertently shut down, thinking the 
valves were open.  Since it was a secondary main, the fire pumps were fine, but 
the hydrants wouldn't function for fire flows. Just something to think about 
for all those civil engineers on here...

Jamie Seidl 
Sent from my iPhone