The operating rod won't turn the gate valve? Last time someone jammed the
valve open. If you dump oil down the PIV for lubrication it may allow it the
valve to free up. Use a bigger wrench with longer handle.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Monday, November 24, 2014 9:25 PM
To: [email protected]
Subject: Re: Frozen open PIV

Good question. 
Yes we did and we pulled the top off the post as well to verify it was a
valve issue and not the post. It also was completely covered in ivy leading
us to believe it had not been exercised for many years despite inspection
tags. W

Jeff
JB Fire Protection
Sent from my iPhone

> On Nov 24, 2014, at 18:13, <[email protected]> <[email protected]>
wrote:
> 
> Did you check to see if it is a left hand valve? I've run into this in the
past. 
> 
> Mark at Aero
> 602 820-7894
> 
> Sent from my iPhone
> 
>> On Nov 24, 2014, at 6:08 PM, "Jeff Bridges" <[email protected]>
wrote:
>> 
>> We have a Post indicator valve that controls a single interior riser.
>> 
>> We discovered during routine testing the PIV is frozen.
>> 
>> The sign indicates it's in the open position and main drain test 
>> shows no abnormalities from previous inspections.
>> 
>> We proposed replacing the PIV and valve- another company proposed 
>> yanking the post, leaving the valve and simply adding a BFV on the riser.
>> 
>> Acceptable alternative?
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to