> On Dec 3, 2014, at 10:37 AM, Travis Mack <[email protected]> wrote:
> 
> This is an interesting issue on the FDC.  My understanding is the FDC on a 
> *sprinkler *system is not required to accommodate the largest sprinkler 
> demand.  It is a supplement to the main water supply.  Otherwise, we would be 
> calculating the FDC piping for all systems, like we do a manual standpipe 
> system.
> 
> For example, is a fire dept connection required to be sized to supply an ESFR 
> sprinkler system with 45' of storage and K25 ESFR sprinklers?  If so, that 4" 
> FDC put on the building is not near adequate.  Now, I am not saying it is not 
> a bad idea, and we are always allowed to do more than the minimum required by 
> NFPA 13. But, I don't believe that NFPA 13 mandates that the FDC be capable 
> of fully supplying the fire sprinkler systems. Note: This does not stand true 
> for manual standpipe systems.
> 
> Travis Mack, SET