I read that Jack, just curious what it said. It doesn't seem to indicate a 
requirement to use any particular system, only requires when you need a fire 
suppression system.

What I found was in A.8.6.2.2.1 which says, "Wet pipe, dry pipe, and pre-action 
systems area acceptable... but are not recommended for the power area, main 
distribution frame (MDF) areas, signal processing area, and standby engine 
areas."

If he is referencing this I have a problem with it since this indicates an 
actual telecommunications facility associated with what I would call "mission 
critical" equipment. These are just rooms on each floor. If the 
telecommunications rooms serve areas in the hospital that are running critical 
lifesaving equipment and interface with other equipment then perhaps, but if 
it's just telephone/internet/data access I don't see a concern.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Fairchild, Jack
Sent: Saturday, December 06, 2014 8:24 PM
To: [email protected]
Subject: RE: FM 200 AND CO2

Look in NFPA 76.

Jack Fairchild


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Engr. belal alrwadieh
Sent: Saturday, December 06, 2014 3:39 AM
To: [email protected]
Subject: Re: FM 200 AND CO2

I'm working as a contractor, and our consultant insist that it is shown in NFPA 
for communication Room is a must to install Clean Agent Fire Suppression 
systemi can not understand this  Eng Belal K. AlrwadiehMSc Design Of Steel 
StructureBSc Mechanical Engineering Address:  KSA-RiyadhAl-Yarmouk, Abu Ja'afr 
AlmansourJordan-AmmamTabrbour-Alkhazna NeighborhoodAlkhaldeen St-Bldg 32h email 
Address:[email protected] Mobile Number:KSA-+966-549-326055Jordan: 
+962-776-498924               +962-795-630998 

     On Wednesday, December 3, 2014 4:23 PM, "[email protected]" 
<[email protected]> wrote:
   

 There is no conditions where FM200 MUST be used.  That is why you didn't find 
any such statement.

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Engr. belal alrwadieh
Sent: Tuesday, December 02, 2014 11:46 PM
To: [email protected]
Subject: FM 200 AND CO2

Gents,
I was trying to find clear statement to describe when the clean agent 
considered as a must to be used but i could nt find.

Can any support if there is any

I read in NFPA 2001 A recommendation for usage but not a rule to follow

Sent from Yahoo Mail on Android

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to