I read that Jack, just curious what it said. It doesn't seem to indicate a requirement to use any particular system, only requires when you need a fire suppression system.
What I found was in A.8.6.2.2.1 which says, "Wet pipe, dry pipe, and pre-action systems area acceptable... but are not recommended for the power area, main distribution frame (MDF) areas, signal processing area, and standby engine areas." If he is referencing this I have a problem with it since this indicates an actual telecommunications facility associated with what I would call "mission critical" equipment. These are just rooms on each floor. If the telecommunications rooms serve areas in the hospital that are running critical lifesaving equipment and interface with other equipment then perhaps, but if it's just telephone/internet/data access I don't see a concern. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Fairchild, Jack Sent: Saturday, December 06, 2014 8:24 PM To: [email protected] Subject: RE: FM 200 AND CO2 Look in NFPA 76. Jack Fairchild -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Engr. belal alrwadieh Sent: Saturday, December 06, 2014 3:39 AM To: [email protected] Subject: Re: FM 200 AND CO2 I'm working as a contractor, and our consultant insist that it is shown in NFPA for communication Room is a must to install Clean Agent Fire Suppression systemi can not understand this Eng Belal K. AlrwadiehMSc Design Of Steel StructureBSc Mechanical Engineering Address: KSA-RiyadhAl-Yarmouk, Abu Ja'afr AlmansourJordan-AmmamTabrbour-Alkhazna NeighborhoodAlkhaldeen St-Bldg 32h email Address:[email protected] Mobile Number:KSA-+966-549-326055Jordan: +962-776-498924 +962-795-630998 On Wednesday, December 3, 2014 4:23 PM, "[email protected]" <[email protected]> wrote: There is no conditions where FM200 MUST be used. That is why you didn't find any such statement. Craig L. Prahl Fire Protection Group Lead CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29303 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Engr. belal alrwadieh Sent: Tuesday, December 02, 2014 11:46 PM To: [email protected] Subject: FM 200 AND CO2 Gents, I was trying to find clear statement to describe when the clean agent considered as a must to be used but i could nt find. Can any support if there is any I read in NFPA 2001 A recommendation for usage but not a rule to follow Sent from Yahoo Mail on Android _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org