Do not supply the jockey pump power supply connection from inside the fire pump panel as I have seen before.
Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of AKS-Gmail-IMAP Sent: Monday, December 29, 2014 9:43 PM To: [email protected] Subject: Re: JOCKEY PUMP ELECTRIC CONNECTION No rule, but use the emergency circuit. Otherwise, when the power is out and life is getting frantic because of that, you don’t want the fire pump to come on when instead the jockey pump could have come on. There would already be enough trouble happening. Somebody will be looking to ask why you put normal power to the jockey pump when you also had emergency power. Allans Seidel St. Louis, MO > On Dec 29, 2014, at 5:55 PM, Cesar Lira <[email protected]> wrote: > > In a pumps room we have two electrical circuits the normal electricity > and the emergency circuit but What is than importan tie a jockey pump > to emergency circuit. > Or there are some rule ore cedes where it indicates where is more > favorable connect the jockey pump or if I can connect to normal circuit. > > Regards. > CLR > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org