Do not supply the jockey pump power supply connection  from inside the fire 
pump panel as I have seen before.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of AKS-Gmail-IMAP
Sent: Monday, December 29, 2014 9:43 PM
To: [email protected]
Subject: Re: JOCKEY PUMP ELECTRIC CONNECTION

No rule, but use the emergency circuit. Otherwise, when the power is out and 
life is getting frantic because of that, you don’t want the fire pump to come 
on when instead the jockey pump could have come on. There would already be 
enough trouble happening. Somebody will be looking to ask why you put normal 
power to the jockey pump when you also had emergency power.  

Allans Seidel
St. Louis, MO

> On Dec 29, 2014, at 5:55 PM, Cesar Lira <[email protected]> wrote:
> 
> In a pumps room we have two electrical circuits the normal electricity 
> and the emergency circuit but What is than importan tie a jockey pump 
> to emergency circuit.
> Or there are some rule ore cedes where it indicates where is more 
> favorable connect the jockey pump or if I can connect to normal circuit.
> 
> Regards.
> CLR
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to