I was always under the impression that you could use a standard spray pendent/upright anywhere, and that it was the designers option to use the CCS sprinklers or just a standard spray pendent/upright. (NFPA 2007 8.4.1.1 "upright and pendent spray sprinklers shall be permited in all occupancy hazard classifications and building construction types.)
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack Sent: Wednesday, January 14, 2015 4:25 AM To: [email protected] Subject: Re: Interstitial Space Between Floors If space is <36" clear (54" max) and slope is <2:12 then they are needed. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone > On Jan 13, 2015, at 10:47 AM, Jay White <[email protected]> wrote: > > Are you required to use the Specific Application Sprinklers for > Combustible Concealed Spaces between floors? Or can you use a standard > quick response upright? > > > > Jay White > > Dynamic Fire Protection > > 9771 Highway 25 South > > Starkville, MS 39759 > > PH: 662-312-2426 > > FAX: 662-324-1545 > > > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org