8.10.3.4 Residential sidewall sprinklers shall be permitted to be
installed on opposing or adjacent walls, provided no sprinkler is
located within the maximum protection area of another sprinkler
or unless separated by baffles that comply with the following:
(1) Baffles shall be arranged to protect the actuating elements.
(2) Baffles shall be of solid and rigid material that will stay in
place before and during sprinkler operation.
(3) Baffles shall be not less than 8 in. (203 mm) long and 6 in.
(152 mm) high.
(4) The tops of baffles shall extend between 2 in. and 3 in.
(51 mm and 76 mm) above the deflectors.
(5) The bottoms of baffles shall extend downward to a level at
least even with the deflectors.

Peter Schwab
VP of Purchasing & Engineering Technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Monday, January 19, 2015 10:07 PM
To: [email protected]
Subject: residential sidewall sprinklers

In the section on standard spray sidewall sprinklers, NFPA 13 prohibits 
sidewall sprinklers being on adjacent or opposing walls if they are in the 
spray pattern of another sidewall.  Does this prohibition exist for residential 
sidewall sprinklers? I can not seem to locate it if it does.  I am reviewing a 
set of plans and this comment was brought up.  I wanted to have a section of 
the standard to verify if the requirement does exist.  Can anyone help with the 
section reference, or help confirm that it is not in the section on residential 
sidewall sprinklers?

Thanks!

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to