All of this assuming that the ceiling is FLAT. Remember that the listings for sidewall sprinklers installed up or across sloped ceilings have all been pulled.
This may or may not be relevant, but I haven't posted in a while and feel left out. SL -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Pete Schwab Sent: Tuesday, January 20, 2015 4:41 AM To: [email protected]; [email protected] Subject: RE: residential sidewall sprinklers 8.10.3.4 Residential sidewall sprinklers shall be permitted to be installed on opposing or adjacent walls, provided no sprinkler is located within the maximum protection area of another sprinkler or unless separated by baffles that comply with the following: (1) Baffles shall be arranged to protect the actuating elements. (2) Baffles shall be of solid and rigid material that will stay in place before and during sprinkler operation. (3) Baffles shall be not less than 8 in. (203 mm) long and 6 in. (152 mm) high. (4) The tops of baffles shall extend between 2 in. and 3 in. (51 mm and 76 mm) above the deflectors. (5) The bottoms of baffles shall extend downward to a level at least even with the deflectors. Peter Schwab VP of Purchasing & Engineering Technologies Wayne Automatic Fire Sprinklers Inc. 222 Capitol Court Ocoee, Fl 34761 Mobile: (407) 468-8248 Direct: (407) 877-5570 Fax: (407) 656-8026 www.waynefire.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack Sent: Monday, January 19, 2015 10:07 PM To: [email protected] Subject: residential sidewall sprinklers In the section on standard spray sidewall sprinklers, NFPA 13 prohibits sidewall sprinklers being on adjacent or opposing walls if they are in the spray pattern of another sidewall. Does this prohibition exist for residential sidewall sprinklers? I can not seem to locate it if it does. I am reviewing a set of plans and this comment was brought up. I wanted to have a section of the standard to verify if the requirement does exist. Can anyone help with the section reference, or help confirm that it is not in the section on residential sidewall sprinklers? Thanks! -- Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org