I have always just done cowboy math to give them a rough idea of delivery time. 
Volume of system piping/demand gpm=approximate time (500 gallon volume/1000 gpm 
demand = .5x60=30 seconds) to get water to the last generator. There will 
typically be at least one timed discharge test with just water and another with 
foam so the calculated time is really of no consequence.

They usually want to see the flow for the overhead sprinkler system "simulated" 
during the HEF test by discharging the calculated supply gpm from the test 
header. It can be a little tricky if the pull station used to activate the 
system also starts the pumps. We would flow the test header before the test and 
wire the valve handles in position after the required flow was achieved. Then 
close the test header control valve. When the deluge valve tripped for the test 
we would quickly open the test header control valve to simulate both HEF and 
sprinkler flow together.
Ron F

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Fairchild, Jack
Sent: Friday, January 30, 2015 12:31 PM
To: [email protected]
Subject: RE: foam delivery times

I met with Mike Mohomet and the rest of the sprinkFDT group while working on my 
Great Adventure analysis.  They told me the programs listing limited them to 
four heads.