Fire retardant does not equal fire proof or non-combustible.  For a lot of 
commodities such as this all it means is that the material burns when in direct 
contact with flame but will self-extinguish when a flame is removed.  They will 
also meet the smoke/flame spread ratings to be called a fire retardant 
material.   The designation for fire resistant EPS is EPS-SE, this stuff still 
degrades, melts, burns and gives off fumes but ignition requires a higher 
temperature and the material will self-extinguish when the ignition source is 
removed.

It's interesting that they would go the route of using HBCD with the ongoing 
EPA investigations into health and environmental concerns related to the 
material.  There was a draft report published by the EPA in 2013 looking at 
alternatives to the use of HBCD.

If it was me, I would not downgrade any level of protection one bit.  I'd treat 
it like EPS and move on since there is no documented testing that I could find 
stating a change in the design criteria was appropriate due to the fire 
resistance nature of the material.  The only difference in the FR and non-FR 
materials was the ignition temperatures and shrinkage under a fire condition.  
Both ended up in liquid form, both emitted combustible and toxic fumes and 
smoke.  

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Monday, February 02, 2015 2:17 PM
To: [email protected]
Subject: fire retardant treated plastic foam

I am looking at a warehouse storing expanded polystyrene building insulation. 
Normal plastic foam is a pretty clear cut group A plastic, however, this foam 
has a fire retardant treatment in it so that it can be used for construction. 
(the chemical used is HBCD)

Anyone heard of any studies or info regarding how this should be protected? 
Still a group A expanded plastic, or does the FR incorporated into it reduce 
the commodity rating?
 
Thanks!

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to