Can not agree more: "Retard" means delay, hence ignition is delayed not
stopped or eliminated.
You may also like to note the reference from Treaties
(https://treaties.un.org/doc/Publication/CN/2013/CN.934.2013-Eng.pdf) that
"HBCD is listed for elimination, but with a specific exemption for expanded
polystyrene (EPS) and extruded polystyrene (XPS) in buildings. Countries may
choose to use this exemption for up to five years after the request for
exemption is submitted. Japan was the first country to implement a ban on
the import and production of HBCD effective in May 2014." So in a few years
the building may need to remove this material.
EPS-SE is still EPS hence need proper protection.

Cheers
Jack C KILAVUZ

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Tuesday, 3 February 2015 6:56 AM
To: [email protected]
Subject: RE: fire retardant treated plastic foam

Fire retardant does not equal fire proof or non-combustible.  For a lot of
commodities such as this all it means is that the material burns when in
direct contact with flame but will self-extinguish when a flame is removed.
They will also meet the smoke/flame spread ratings to be called a fire
retardant material.   The designation for fire resistant EPS is EPS-SE, this
stuff still degrades, melts, burns and gives off fumes but ignition requires
a higher temperature and the material will self-extinguish when the ignition
source is removed.

It's interesting that they would go the route of using HBCD with the ongoing
EPA investigations into health and environmental concerns related to the
material.  There was a draft report published by the EPA in 2013 looking at
alternatives to the use of HBCD.

If it was me, I would not downgrade any level of protection one bit.  I'd
treat it like EPS and move on since there is no documented testing that I
could find stating a change in the design criteria was appropriate due to
the fire resistance nature of the material.  The only difference in the FR
and non-FR materials was the ignition temperatures and shrinkage under a
fire condition.  Both ended up in liquid form, both emitted combustible and
toxic fumes and smoke.  

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Matt Grise
Sent: Monday, February 02, 2015 2:17 PM
To: [email protected]
Subject: fire retardant treated plastic foam

I am looking at a warehouse storing expanded polystyrene building
insulation. Normal plastic foam is a pretty clear cut group A plastic,
however, this foam has a fire retardant treatment in it so that it can be
used for construction. (the chemical used is HBCD)

Anyone heard of any studies or info regarding how this should be protected?
Still a group A expanded plastic, or does the FR incorporated into it reduce
the commodity rating?
 
Thanks!

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.5646 / Virus Database: 4273/9047 - Release Date: 02/02/15

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to