I recently and changed a check valve for the fdc on a single dry system that 
was installed after the dry valve. The system wasn't very old and the check 
valve was very eroded. A.8.16.1.1 shows valve arrangements.

Sent from my Verizon Wireless 4G LTE smartphone

<div>-------- Original message --------</div><div>From: John Denhardt 
<[email protected]> </div><div>Date:02/05/2015  3:19 PM  (GMT-07:00) 
</div><div>To: "'[email protected]'" 
<[email protected]>,SprinklerFORUM 
<[email protected]> </div><div>Subject: RE: FDC on a dry system 
</div><div>
</div>
Well????



You are correct based on the intent of NFPA 13 IN MY HONEST OPINION.  However, 
8.17.2.4.1.2 (2013) stated that attaching to a main is okay.  This is a 
sub-section to 8.17.2.4.1 - The fire department connection shall be on the 
system side of the water supply check valve.  And the main you are tying into 
complies but there is a dry valve in between.



The practical issue is that the fire department connection most likely will 
leak pressurized air that is on the dry pipe system piping.  What is going to 
keep the fire department connection check valve air tight?  Is the rubber going 
to dry out?



John





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gregory Lindholm
Sent: Thursday, February 05, 2015 5:01 PM
To: SprinklerFORUM
Subject: FDC on a dry system



I always went by having to take the supply for the FDC, from a tee between the 
system control valve, and the dry pipe valve. (On a single dry pipe system). 
NFPA #13 - 2010, 8.17.2.4.2(2) states it this way.

8.17.2.4.1.2 says that it can be connected to the main piping on the system it 
serves, ie: the end of a cross main.

I always believed that taking off the end of the cross main only applied to wet 
pipe systems. I am not agreeing with somebody that says that it can come off 
the end of the main on a dry system also.

What am I missing, or have I been wrong?



Greg Lindholm

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to