Here’s the way to look at it.  What in 8.17.2.4.1.2 says you can ignore any 
other requirements such as 8.17.2.4.2(2)?  It doesn’t so it still applies.

It would have been cleaner if the TC had said in 8.17.2.4.1.2 the FDC on wet 
pipe system can be connected to the main. IF they had meant to allow it on Dry 
systems, they need to modify the other applicable sections.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Feb 5, 2015, at 2:01 PM, Gregory Lindholm <[email protected]> wrote:
> 
> I always went by having to take the supply for the FDC, from a tee between 
> the system control valve, and the dry pipe valve. (On a single dry pipe 
> system). NFPA #13 - 2010, 8.17.2.4.2(2) states it this way. 
> 8.17.2.4.1.2 says that it can be connected to the main piping on the system 
> it serves, ie: the end of a cross main. 
> I always believed that taking off the end of the cross main only applied to 
> wet pipe systems. I am not agreeing with somebody that says that it can come 
> off the end of the main on a dry system also.
> What am I missing, or have I been wrong?
> 
> Greg Lindholm                                           
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to