I don't think you have to CHECK (emphasis not shouting) for leaks.  IF you see 
them that is a loss. 

25.2.1.1 ....and shall maintain that pressure without loss for 2 hours.  So I 
read the requirement is hold pressure.  Holding pressure is defined in:

25.2.1.7 Loss (my words loss of pressure) shall be determined by a drop in 
gauge pressure or visual leakage.

Leakage came about because fitters would argue they passed because the leak was 
so small the gauge didn't move (or they used the stuck gauge).  For some reason 
I don't think this was in the early '90's editions because that's when I was 
the AHJ and I had this discussion more than once.  I would have said see 
25.2.1.7 (or whatever section it was back then) and call me when you fix the 
leak.  I'd look it up but I don't have old versions handy.  If it was in code I 
wouldn't have had to explain many times the fundamental fact you are not 
holding pressure if anything is leaking at any rate.  Maybe after 2 hours you 
are at 0.001 psi loss but that's still a loss of pressure not permitted.  
Because I can't measure the loss with a 300 psi gauge doesn't mean it wasn't 
losing pressure. No I didn't have a gauge to that accuracy and temperature 
fluctuations are more than 0.001 probably.  

If it's leaking even a small leak there will be water stains in the tile or 
sheet rock.  Is it possible a leak could be so small it doesn't wet anything in 
2 hrs, probably. But let's go back to the purpose of the test. It's not really 
there for small issues, it's will it catastrophically come apart.  A weeper at 
a thread isn't going to fail the system (for a long time anyway).  Weepers even 
if missed are going to be caught by the owner at some point and will be 
repaired under warranty.  

If exposed piping were required the standard it should/would come out and say 
it not say one thing in x.1 and hide exposed pipe in x.7.  I don't for a second 
think that is what they meant.  Of course I was wrong when I got out of bed 
this morning so it stands to reason I'd could be wrong again. 

Is it better to do a hydro with the piping exposed, for my money no doubt, job 
schedule doesn't always make this easy. As an AHJ it's up to the contractor, I 
only need to see one test and I concede plugs on the drops are OK.  Missing 
drops not so much.   

I'd also like to point out that section 25.2.1.11 is odd in addition to being 
new.  So can I put sidewalls in upright or pendant outlets for testing?  Were 
they trying to say uprights had to be in for testing where uprights were used?  
That's not what they said. If I plug an upright do I have to remove it after 
testing? If I put a pendant in an upright outlet can it stay?

25.2.1.11 proves IMHO the intent of the test really is big issues otherwise 
you'd have to test with heads in.  Theoretically, the standard allows all heads 
to leak at the fitting or cap.  There isn't a way to really quantify big leaks 
from little leaks from a hydro.   

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Denhardt
Sent: Wednesday, March 11, 2015 4:54 PM
To: <[email protected]>
Subject: Re: Multiple Hydrostatic Tests

Chris - how do you check for visible leaks if you can not see the concealed 
piping?

Sprinklers Save

> On Mar 11, 2015, at 5:49 PM, "Cahill, Christopher" <[email protected]> 
> wrote:
> 
> I agree with IOR. But only one needs to be done when the work is complete. 
> The confusion may be a false belief the test needs to be done with exposed 
> pipe. There is no such requirement.
> 
> Chris Cahill
> Fire Protection Engineer
> Burns & McDonnell
> [email protected]
> 952-656-3652 Gary Stites wrote:
> We have run across an interesting situation at a California Hospital. 
> The IOR is suggesting that we will be required to hydro the systems 
> twice, once at rough-in for a "performance test" and again near final 
> as an "acceptance test". His logic is that all appurtenances are not 
> installed and in place at the time of rough-in which is required by 
> the code, thus removing plugs and installing sprinklers in flex drops 
> he considers a significant modification or "more than a minor" modification, 
> so test twice.
> 
> 
> Anybody have any interpretations or documents that would refute this?
> 
> 
> Gary Stites
> *805-769-GMAN*
> RLH <http://www.rlhfp.com>
> Google+ <https://plus.google.com/101832074405776300082/posts?hl=en>
> Mr. Ricky <http://www.mrricky.net>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to