Yes..QR reduction permitted. We take the height based on the distance from the lowest ceiling to the peak. Remember to take the 30% increase for sloped ceilings.

One thing to consider. You are going to be limited to 120 sq ft per sprinkler. Consider using 4.2k SSU (light hazard wet pipe) as it will greatly minimize the over-discharge and therefore friction losses in your system.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 3/16/2015 11:26 AM, [email protected] wrote:
Here's one for Y'all.
With a wet-pipe system in an attic, (4/12 pitch) can the area reduction for 
quick response sprinklers be used?
If so, how is the ceiling height determined? From the ceiling below to the 
highest point of the roof?
Thanks
Bill