You can take the reduction for QR, but also have to increase for the slope; 
it's a compound DA calculation.

Steve Leyton




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, March 16, 2015 11:26 AM
To: sprinklerforum
Subject: QR reduction in attic?

Here's one for Y'all. 
With a wet-pipe system in an attic, (4/12 pitch) can the area reduction for 
quick response sprinklers be used? 
If so, how is the ceiling height determined? From the ceiling below to the 
highest point of the roof? 
  
Thanks 
Bill 



  