You can use the criteria for 35' max ceiling height - since 32' is less than 
the max allowed.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 
 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Wednesday, March 18, 2015 1:59 PM
To: [email protected]
Subject: RE: ESFR & Storage

Table 16.2.3.1 for 25' storage height & 32' ceiling specifies either 14.0k or 
16.8k heads.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Wednesday, March 18, 2015 2:44 PM
To: [email protected]
Subject: Re: ESFR & Storage

Why wouldn’t you use the K-25 and apply 20 psi?


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Mar 18, 2015, at 8:04 AM, Brian Harris <[email protected]> wrote:
> 
> Excuse me if this is a dumb question but I'm doing a large warehouse that 
> falls under table 16.2.3.1 (2007) with 25' storage & max ceiling of 32'. 
> Looks like I can use either 14.0k or 16.8k heads. What's the reason I 
> couldn't use the 25.2K heads and save on end head pressure?
> 
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to