DING DING DING. We have a winner. Historically ESFR has no limit on clearance. It is simply an Up to on Ceiling height and up to on storage height. Anything below the two maximums is applicable. That is how the criteria is still applied but behind the scenes clearance has become an issue (as to whether the allowance is allowed in the standard aka it applies to both new criteria being added or existing criteria being allowed to remain.)
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Mar 18, 2015, at 11:59 AM, Matt Grise <[email protected]> wrote: > > You can use the criteria for 35' max ceiling height - since 32' is less than > the max allowed. > > Matt Grisé PE*, LEED AP, NICET II > Sales Engineer > Alliance Fire Protection > 130 w 9th Ave. > North Kansas City, MO 64116 > > *Licensed in KS & MO > > 913.888.0647 ph > 913.888.0618 f > 913.927.0222 cell > www. AFPsprink.com > > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Brian Harris > Sent: Wednesday, March 18, 2015 1:59 PM > To: [email protected] > Subject: RE: ESFR & Storage > > Table 16.2.3.1 for 25' storage height & 32' ceiling specifies either 14.0k or > 16.8k heads. > > Brian Harris, CET > BVS Systems Inc. > bvssytemsinc.com > > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Roland Huggins > Sent: Wednesday, March 18, 2015 2:44 PM > To: [email protected] > Subject: Re: ESFR & Storage > > Why wouldn’t you use the K-25 and apply 20 psi? > > > Roland Huggins, PE - VP Engineering > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives > Dallas, TX > http://www.firesprinkler.org <http://www.firesprinkler.org/> > > > > > >> On Mar 18, 2015, at 8:04 AM, Brian Harris <[email protected]> wrote: >> >> Excuse me if this is a dumb question but I'm doing a large warehouse that >> falls under table 16.2.3.1 (2007) with 25' storage & max ceiling of 32'. >> Looks like I can use either 14.0k or 16.8k heads. What's the reason I >> couldn't use the 25.2K heads and save on end head pressure? >> >> Brian Harris, CET >> BVS Systems Inc. >> Sprinkler Division >> bvssystemsinc.com<http://bvssystemsinc.com/> >> Phone: 704.896.9989 >> Fax: 704.896.1935 >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org