I don't know what your AHJ is going to ask for James, however you might find some guidance in 11.2.1(1) which covers adjacent hazards or design methods, and requires the more demanding design to extend 15'-0" beyond if there's no barrier separating them. Sub items (2) and (3) might be helpful as well. I seem to remember similar language in 12.3 (1)-(2) and (3) also.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/>

***
On 3/19/2015 9:40 AM, James Crawford wrote:
We are doing an addition to an existing warehouse, the existing warehouse is
protected with ESFR K14 uprights, since the building was constructed the AHJ
has dropped the water pressures in the area by 10 psi.

Due to the pressure drop I cannot use the K14 heads for the addition, can
you mix ESFR sprinkler heads in the same warehouse area, I would need K17
heads for the addition, The addition would be open to the existing warehouse
space. Or do I need to change all the heads in the existing warehouse to
match?

Thank you

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected]