We always split the systems where the K factor changes. However, if the 
addition is small the total area is under 40k sqft you would probably have to 
change all the heads on that system to K17.
Ron F 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Crawford
Sent: Thursday, March 19, 2015 11:21 AM
To: [email protected]
Subject: RE: ESFR Sprinkler Heads

Thanks Roland

The AHJ has impose a greater reduction and if I use the new pressures the 
existing system is 3 psi short.

My concern with using two different K factor heads is the overlap area where 
two different pressures would be required causing over discharge on the K17 
heads.


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  [email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Thursday, March 19, 2015 11:05 AM
To: [email protected]
Subject: Re: ESFR Sprinkler Heads

you can have multiple design basis covering different portions of a building.  
They could present different K-factors or types of sprinklers.
There are explicit requirements that address the interface between them.

What do you mean the AHJ has dropped the pressure?  Does that mean the water 
purveyor has dropped the pressure to the area or that the AHJ has imposed a 
greater reduction on the actual supply as a safety factor.  In other words, is 
the existing system still providing adequate protection (not an issue for 
imposed reductions) ?


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Mar 19, 2015, at 9:40 AM, James Crawford <[email protected]>
wrote:
> 
> We are doing an addition to an existing warehouse, the existing 
> warehouse is protected with ESFR K14 uprights, since the building was 
> constructed the AHJ has dropped the water pressures in the area by 10 psi.
> 
> 
> 
> Due to the pressure drop I cannot use the K14 heads for the addition, 
> can you mix ESFR sprinkler heads in the same warehouse area, I would 
> need K17 heads for the addition, The addition would be open to the 
> existing warehouse space. Or do I need to change all the heads in the 
> existing warehouse to match?
> 
> 
> 
> 
> 
> Thank you
> 
> 
> 
> 
> 
> James Crawford
> 
> Phaser Fire Protection Ltd.
> 
> Phone  604-888-0318
> 
> Fax 604-888-4732
> 
> Cel 604-790-0938
> 
> Email  [email protected]
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to