The Class increase mentioned applies to commodities stored on non-FM approved 
plastic pallets not those commodities stored IN plastic containers.

The weight of an empty barrel is irrelevant, it would classified as Group A 
automatically if it was empty.

If you take a look over at FM Data sheet 8-1 Commodity Classification #160 
Powders/Granulars, free flowing inert materials in combustible bags it's 
considered a Class I
Then look at #122 "Plastic Containers- Plastic containers, solid or gridded, 
storing combustible solids that would be considered Class 1, 2, 3, or 
unexpanded plastics, all volumes, completely
Full - Class UUP.  UUP is considered Uncartoned, Unexpanded, Plastic.  Per this 
data she in 2.3.8.3 " In general, plastic storage containers drive the fire 
protection. Treat the commodity as follows when storing the materials as 
described."  - UUP - Noncombustible solids in containers greater than 1 gal (4 
L) in volume."

NFPA 13 Table A.5.6.3 for non-combustible liquids (yes I know were talking 
granulars but key in on non-combustible) in plastic containers with nominal 
wall thickness greater than 1/4" and larger than 5 gallons = Group A

So if you follow the recommendations and direction provided across multiple 
Design standards you will be led back to considering this configuration as 
Group A plastics.

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Crawford
Sent: Thursday, March 26, 2015 2:21 PM
To: [email protected]
Subject: RE: absorbant in plastic drums

Powder in a paper bag is a class 2

Put it into a plastic barrel, similar to a plastic pallet you would increase 
two classes to a class 4 commodity

Class 4 contains within itself or it's packaging an appreciable amount (5 to 
15% by weight or 5 to 25% by volume) of group A plastics. What is the weight of 
an empty barrel?

Seems to fall in this range.



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  [email protected]




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Thursday, March 26, 2015 9:02 AM
To: [email protected]
Subject: RE: absorbant in plastic drums

The plastic drum will end up driving the design criteria, so treat it like 
Group A plastics.  




Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Todd - Work
Sent: Thursday, March 26, 2015 11:09 AM
To: [email protected]
Subject: absorbant in plastic drums

I am looking at a job where the product being stored is a granulated
absorbent (think stuff to put on concrete to absorb oil) in 55 gallon
plastic drums. New product, not used. I am teetering between Class IV and
Group A Plastic. Has anyone else working on something like this?

Sent from my iPad
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to