Please clarify,  in one paragraph you stated the system was hydraulically 
calculated but in another you state something was sized by "hydraulic pipe 
schedule".

So is the existing system calculated or scheduled?

Is the water supply exactly the same as it was when the existing system was 
installed?  Has the pipe in the existing system ever had any internal 
inspections for corrosion or other buildup such as MIC?

Why would you not calculate it and remove all doubt about performance and 
compliance?

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tim Stone
Sent: Thursday, April 09, 2015 8:57 AM
To: [email protected]
Subject: Hydraulic Calcs on an existing sprinklered building

Hi,

 

I am working on an existing light hazard building that is being remodeled and 
updated. The four story building (8400SF / floor) was built in 1992 and is 
equipped with a hydraulically calculated sprinkler system. The bulk of the 
sprinkler system work on this project is to relocate sprinkler heads to new 
ceiling layout and relocate a few mains and branchlines to accommodate new 
HVAC. 

 

A 1700 SF. 2 story addition is being built on one side and the sprinkler system 
is to be extended to cover this new space. The existing hydraulic pipe schedule 
already in place is going to be used to extend the system into the addition.

 

Is it required to perform Hydraulics on this 1700SF addition? 2010 ed. of NFPA 
13, 22.4 does not indicate that it is.

 

Am I missing something?

 

Thank you in advance.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343

                            <mailto:[email protected]> [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to