Does the owner pay you to do it annually, every three years, or at all. Whatever you contract to do is what you do. You use the appropriate form and if it's a due item you mark it as not done, or if it fails.... If he doesn't want to pay for any part you handle it the same way. it's his responsibility to have things done. It's yours to do what he asks you to do. You can advise him but ultimately it's his prerogative to take or leave your advice.
On Wed, Apr 15, 2015 at 9:50 AM, Jay Stough <[email protected]> wrote: > I have a question about the 3 year air test required for dry, deluge and > preaction systems by NFPA 25 (2011 or 2014) 13.4.3.2.6 (preaction, deluge) > or 13.4.4.2.9 (dry systems). I know I probably have the only customer that > does not address the leaks after a failed test, so how would you handle the > test? We record it as a failed test. Do you repeat the test annually > until you get a satisfactory test; or just repeat the test in three years? > After reading the above paragraphs, I could not find any guidance, in the > standard or the handbook. > > *Jay Stough* > NICET IV LAYOUT > NICET III ITM > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org