Sorry, I forgot the ;-). But if it's an FM account, the FM Field Engineer 
should be helpful in weighing in on the high air exchange rate for the 
facility.  

Mark at Aero
602 820-7894

Sent from my iPhone

> On Apr 23, 2015, at 6:53 AM, "Tim Stone" <[email protected]> wrote:
> 
> Mark,
> It is a FM job and the Fire Protection engineer has specified the HCs for
> the project.
> The ventilation system and it negative effect on sprinkler head operation is
> what concerns me.
> 
> Regards,
> G. Tim Stone
> 
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
> 
>                 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                            [email protected]
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of [email protected]
> Sent: Thursday, April 23, 2015 9:42 AM
> To: [email protected]
> Subject: Re: Cow Barn Ventilation
> 
> The first question you must answer is, "are cows ordinary hazard group  II,
> or Class III Commodity?"  
> 
> Mark at Aero
> 602 820-7894
> 
> Sent from my iPhone
> 
>> On Apr 23, 2015, at 5:39 AM, "Tim Stone" <[email protected]> wrote:
>> 
>> I am in the early stage of Sprinkler design for a new Research Cow 
>> Barn and Milking Parlor.
>> 
>> 
>> 
>> It is a Wood Frame Structure with a 4:12 pitich roof. The barn and 
>> milking parlor both have finished ceilings at [13'-6] above a concrete
> slabs.
>> 
>> 
>> 
>> The Barn and Milk Parlor are to be equipped with Ventilation equipment 
>> consisting of 6- 30,000 CFM, 1 - 86,000 CFM directional flow 
>> circulation fans mounted/suspended at the ceiling, 4 - 72" wall 
>> mounted exhaust fans at one end of the barn.
>> 
>> Also there are 14 automatically actuated ceiling air inlets in the cow 
>> barn and another 8 manually actuated inlets in the Milking parlor.
>> 
>> 
>> 
>> There is no indication on the Electrical or Mechanical Bid Documents 
>> that the ventilation system is tied into the Fire Alarm Panel. I have 
>> submitted a RFI to the General Contractor asking just this question.
>> 
>> 
>> 
>> My question to you is, In a warehouse the ventilation system is tied 
>> in to the fire alarm for shutdown. Shouldn't this Research Cow Barn be 
>> treated the same way?
>> 
>> 
>> 
>> Thank you in advance.
>> 
>> 
>> 
>> Regards,
>> 
>> G. Tim Stone
>> 
>> 
>> 
>> G. Tim Stone Consulting, LLC
>> 
>> NICET Level III Engineering Technician
>> 
>> Fire Protection Sprinkler Design
>> 
>> and Consulting Services
>> 
>> 
>> 
>>               117 Old Stage Rd. - Essex Jct., VT. 05452
>> 
>> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>> 
>>                           <mailto:[email protected]> 
>> [email protected]
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to