Apology accepted ;)

a real head-scratcher--- i thought of a few things, looked them up, and by
golly they were not codes that allows you to design that way (the way we all
do all systems that is)

i'm going home and let this bother me all night... thanks
(i cant wait til tomorrow morning when i check my mail)

brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jack Carlson
Sent: Tuesday, May 05, 2015 4:51 PM
To: [email protected]
Subject: RE: Light & OH1 Hazard From Same Riser

John,

You should not have an issue with the design as described.  Light and
ordinary are commonly mixed, no separate supply main is necessary.


Jack W. Carlson, SET
Triple "A" Fire Protection
Office - 251.649.2034
Fax - 251.649.2037
Cell - 706.247.5050

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Allen, CET, CFPS
Sent: Tuesday, May 05, 2015 5:38 PM
To: [email protected]
Subject: Light & OH1 Hazard From Same Riser

I apologize for such a simple question, but I would greatly appreciate some
guidance: 

I have a 22,000 sqf light hazard office space with a 750 sqf mechanical room
that I've identified as ordinary hazard 1.  The entire ceiling space is an
open 14' concrete beams and roof deck, and the mechanical room is separated
by sheetrock and self-closing doors.  The riser is in the mechanical room
and I have 7 upright sprinkler heads fed off the cross main pipe feeding the
light hazard office space.  What code allows me to design this way or must I
create a separate riser feed for each hazard? 


Best Regards,
 
John Allen, CET, CFPS
President


AFS: Allen Fire & Security
Your Safety is Our Success
Direct: 770.715.7261 | Office: 770.723.7280 Ext 2 | Fax: 678.894.4180 
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to