Okay, I'm really confused.  In NFPA 13HB - 2013, I found the following:

FAQ: Can nonmetallic pipe be used in an ordinary hazard occupancy?
Nonmetallic pipe is not permitted in ordinary hazard occupancies and is only 
permitted in
specific small ordinary hazard rooms within light hazard occupancies. The 
limitation to rooms
that do not exceed 400 ft2 (37 m2) recognizes that almost all buildings have 
typically small
storage rooms or mechanical rooms that would be categorized as ordinary hazard. 
Requiring
a change in pipe type for those rooms or requiring the entire system to use 
metallic pipe
would be overburdensome.

Supplement 3:
(8)* Sprinklers shall not be required to be installed within electrical 
equipment, mechanical
equipment, or air handling units not intended for occupancy.
A.8.1.1(8) Equipment having access for routine maintenance should not be 
considered
as intended for occupancy.
Clarifies that some electrical equipment
is large enough to be accessed by man
doors. In these instances, where this
equipment is not occupied but rather accessed
for maintenance, sprinklers are not
required.

So, my three questions now are: 
1. do I need sprinklers in the mechanical room that is 750 sqf?
2. what code identifies the mechanical room as OH1?
3. if I do need sprinklers, can I design the OH1 area off the cross main that 
feeds the light hazard areas (using only one riser feed)?


Best Regards,
 
John Allen, CET, CFPS
President


AFS: Allen Fire & Security
Your Safety is Our Success
Direct: 770.715.7261 | Office: 770.723.7280 Ext 2 | Fax: 678.894.4180 
 

  Please consider the environment before printing this email 
This email contains proprietary and confidential material for the sole use of 
the intended recipient and is the sole property of AFS.  Any review, use, 
distribution or disclosure by others without the permission of the sender is 
strictly prohibited. If you are not the intended recipient (or authorized to 
receive for the recipient), please contact the sender by reply email and delete 
all copies of the message.


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, May 6, 2015 8:56 AM
To: [email protected]
Subject: RE: Light & OH1 Hazard From Same Riser

You are looking for permission?   How long could the possible scenarios in that 
list be?   

There is no restriction or prohibition of designing systems of different 
densities off one riser.  It's common practice.  Calculate and prove it works 
and you're done.  

Mechanical rooms contain rotating electrical equipment, some may contain 
natural gas or propane piping, or fuel oil, typically there's at least one or 
more boxes of filters since they go with the AC equipment, we will at some time 
probably have to consider the refrigerant being used on HVAC equipment as some 
of the "greener" gases have flammability properties.  So HVAC mechanical rooms 
are not without hazards.  OH 1 is typical for anything bigger than an apartment 
closet mechanical room.

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Tuesday, May 05, 2015 6:14 PM
To: [email protected]
Subject: RE: Light & OH1 Hazard From Same Riser

Apology accepted ;)

a real head-scratcher--- i thought of a few things, looked them up, and by 
golly they were not codes that allows you to design that way (the way we all do 
all systems that is)

i'm going home and let this bother me all night... thanks (i cant wait til 
tomorrow morning when i check my mail)

brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jack Carlson
Sent: Tuesday, May 05, 2015 4:51 PM
To: [email protected]
Subject: RE: Light & OH1 Hazard From Same Riser

John,

You should not have an issue with the design as described.  Light and ordinary 
are commonly mixed, no separate supply main is necessary.


Jack W. Carlson, SET
Triple "A" Fire Protection
Office - 251.649.2034
Fax - 251.649.2037
Cell - 706.247.5050

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Allen, CET, CFPS
Sent: Tuesday, May 05, 2015 5:38 PM
To: [email protected]
Subject: Light & OH1 Hazard From Same Riser

I apologize for such a simple question, but I would greatly appreciate some
guidance: 

I have a 22,000 sqf light hazard office space with a 750 sqf mechanical room 
that I've identified as ordinary hazard 1.  The entire ceiling space is an open 
14' concrete beams and roof deck, and the mechanical room is separated by 
sheetrock and self-closing doors.  The riser is in the mechanical room and I 
have 7 upright sprinkler heads fed off the cross main pipe feeding the light 
hazard office space.  What code allows me to design this way or must I create a 
separate riser feed for each hazard? 


Best Regards,
 
John Allen, CET, CFPS
President


AFS: Allen Fire & Security
Your Safety is Our Success
Direct: 770.715.7261 | Office: 770.723.7280 Ext 2 | Fax: 678.894.4180 
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to