Its ordinary Group 2 ,  based on just that 300 for the system demand . I used 
the in-correct coefficient .  thanks !   
I am going to do another test , luckily in my bad luck  this is close to my 
office . 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: May-07-15 10:14 AM
To: [email protected]
Subject: RE: Flow test - Playpipe w/ 1 1/4" Tips

What is your estimated demand?

Coefficient of Discharge for playpipes is .97---

h= 70/.433=161.66 ft
v=(2gh)^.5=102.03 ft/sec

((1.25/24)^2)*pi= .008522 ft^2, * 102.03 ft/sec= .8695 ft^3/sec, *7.48*60=
390 GPM, * .97= 379 GPM.

Brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Colin Carew (Cambridge)
Sent: Thursday, May 07, 2015 9:03 AM
To: [email protected]
Subject: Flow test - Playpipe w/ 1 1/4" Tips

Hey All ,

I just did a flow test last night .  Instead of flowing just the 2½ butt and 
getting the pitot  pressure like I have done for years , We used (1) Play pipe 
with 1 1/4" Tip . When I convert the pito of 70  to GPM with the 0.90
Coefficient to = 363.41 GPM .    Should I have flowed both sides with two
play pipes to determine a higher flow rate  .  I have an old flow test from
Two years ago that has a flow rate of 1186 Gpm .   I am going to do another
test next week   and just flow the 2½ butt with no playpipes .

Colin

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to