Colin,
I'm assuming that you are talking old school Underwriters Playpipe. If so, to my
knowledge, the standard ripe were 1-3/4 and 1-1/8. Might want to verify the
1-1/4. Also, typically the coefficient is 0.97.
Scott is correct that you want to flow more water than that if you can.
Suggestion: buy a Hosemonster set up. You can get a 2-1/2" calibrated flow,
which is more accurate than an open 2-1-2" butt.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
860-608-4559 (cell)
Sent using CloudMagic 
[https://cloudmagic.com/k/d/mailapp?ct=pi&cv=6.0.64&pv=8.2]
On Thu, May 7, 2015 at 10:08 AM, [email protected]
<[email protected]> wrote:
Colin,

The best case scenario is that you flow more water than your highest anticipated
sprinkler and hose stream, or in the case of a fire department fire flow
requirements. Without knowing your specifics the answer is yes, you should flow
more than 386 gpm.

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of Colin Carew (Cambridge)
Sent: Thursday, May 07, 2015 9:03 AM
To: [email protected]
Subject: Flow test - Playpipe w/ 1 1/4" Tips

Hey All ,

I just did a flow test last night . Instead of flowing just the 2½ butt and
getting the pitot pressure like I have done for years , We used (1) Play pipe
with 1 1/4" Tip . When I convert the pito of 70 to GPM with the 0.90
Coefficient to = 363.41 GPM . Should I have flowed both sides with two play
pipes to determine a higher flow rate . I have an old flow test from
Two years ago that has a flow rate of 1186 Gpm . I am going to do another test
next week and just flow the 2½ butt with no playpipes .

Colin

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to