Hello Greg,

Protect it. We have many of those in this area and have to sprinkler those 
areas.

Tuesday, June 23, 2015, 10:42:31 AM, you wrote:

> Yes and yes...


> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852

> On Tue, Jun 23, 2015 at 9:17 AM, J. Scott Mitchell, PE <[email protected]>
> wrote:



>> Is it accessible? Could it possibly be used for storage?
>> J. Scott Mitchell, PE
>> Sent from my Verizon Wireless 4G LTE smartphone

>> -------- Original message --------
>> From: Greg McGahan <[email protected]>
>> Date: 06/23/2015  9:01 AM  (GMT-06:00)
>> To: [email protected]
>> Subject: open space under concrete building

>> I have an architect asking if protection is required under a high rise
>> building  - noncombustible, if they raise the first occupied floor up so
>> that the "ground floor" is open underneath. There will be nothing
>> obstructing the view from one side to the other except the stairwells and
>> elev shaft basically.

>> I cannot find anything excludes protection....am I missing it?

>> Thanks,


>> Greg McGahan
>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>> 1160 McKenzie Road
>> Cantonment, FL 32533
>> 850-937-1850
>> fax 850-937-1852
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]

>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]

>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



-- 
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to