Steve,

I called him to ask and he said that they are understaffed and he had to
make provisions for less people...




Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852

On Mon, Jun 29, 2015 at 4:35 PM, Steve Leyton <[email protected]>
wrote:

> 1) What do you mean "demanding"?   They just look at every project and
> decide what's required on the spot?
> 4) IBC defines fire areas.  I can't remember the when/where but I'm fairly
> certain that the reference in A.7.10.1.1 is to any fire area as defined by
> the Building Code.  The matrix you sent me includes the prescriptives for
> min. hours of fire resistance required to define fire areas by occupancy
> group.  Fire area size is important because you can create multiple fire
> smaller fire areas to skate on requirements for sprinklers in larger
> "buildings" of "fire areas".  That's part of the code and the standard is
> reactive to that.   Your project description suggest to me that they can be
> separated.
> 5) You have to have two systems (wet and dry) and standpipes on each
> system must be interconnected with each other.  Come out of your pump and
> build two risers ...
>
> It also occurs to me that my last answer was incomplete as I was only
> thinking of Class 1 service in the PG.   Even if you can have a manual
> Class 1, an unsprinklered garage could have a Class 3 system per code and
> the hose stations require an automatic water supply.  Not of the same flow
> and pressure as a Class 1, but automatic nonetheless.   All of it can be
> off of one pump if it's considered one system but the AHJ's mandate could
> be considered contradictory.   You have two separate buildings but they're
> being pushed together as one for system planning.  I dunno man, I guess I'd
> like to know the reasoning behind the automatic requirement for the PG.
>
> My opinion only,
> SML
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Greg McGahan
> Sent: Monday, June 29, 2015 1:44 PM
> To: [email protected]
> Subject: Re: standpipes in fire separated building
>
> Thanks for the reply. Here is the best I can do to articulate my thoughts.
>
> 1) The AHJ is demanding an Auto Standpipe in the Parking Garage and I do
> not know why....but he told the owner that is what he required.
> 2) The PG has only 2 standpipes so no matter what the PG will flow a
> maximum of 750 gpm
> 3) The PG S/Ps are DRY  so they will have to be separate systems to some
> degree, I was going to tie the FDC lines together and use one FDC
> 4) I do not understand the reference in NFPA #14 7.10.1.1 says "Fire Area"
> and the IBC references "Area" in the table I sent you. If that term does
> not apply to this situation, I would like to understand for future
> reference what it applies to. If it does apply, I think we are fine to
> separate the two....
> 5)  If the High Rise s/p's are Auto Wet and the Pg are Auto Dry, which
> they are in this case, what doe that do to interconnection, calcs etc? I
> have never ran into this situation before.
>
>
>
> Greg
>
>
>
>
>
>
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
>
> On Mon, Jun 29, 2015 at 3:28 PM, Steve Leyton <[email protected]>
> wrote:
>
> > I've been out of my office for over a week, so apologies for not
> > acknowledging the calls for my expertise.  I gotta say if it's come
> > down to me, you're all a lot more desperate than I thought ...
> >
> > I notice replies from others on this thread and I think I concur with
> > consensus.   If these are two truly separated buildings (at least as
> > defined by code), are you proposing two separate standpipe systems?
> > Separate response addresses, separate FDC’s?  Or is this going to be
> > one universal system.  Any way you look at it, the parking structure
> > isn’t sprinklered and code would say that you need a Class III with
> 1,250 GPM
> > demand.  The tower would be 750, so garage obviously more demanding.
> If
> > you’re proposing a single automatic water supply/single system
> > configuration, then I’d say it has to meet the 1,250, HOWEVER …
> >
> > Why is the garage required to be automatic.   By definition and open
> > structure, even one taller than 75’ isn’t a high-rise.  Code allows up
> > to
> > 12 tiers without sprinklers if I recall correctly, so the “usual”
> > rules don’t necessarily apply.  My guess is that manual dry is adequate
> – at
> > least per code.   So my answer would be that you should look into a 1,250
> > GPM manual-dry and a 750 GPM auto-wet for the tower (assuming only two
> > stairs).  Is the AHJ or another stakeholder requiring auto-dry in the
> > garage?
> >
> > The foregoing is my opinion only and does not necessarily represent
> > the opinion or intent of the NFPA 14 Technical Committee on Standpipe
> > and Hose Systems.
> >
> > SML
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> > [email protected]] On Behalf Of Richard
> > Matsuda
> > Sent: Monday, June 29, 2015 9:50 AM
> > To: [email protected]
> > Subject: Re: standpipes in fire separated building
> >
> > Greg,I believe the intent of NFPA-14 is to include flow from all the
> > standpipes within a building that the fire dept would connect to in a
> > fire emergency. If the floors in the parking garage do not communicate
> > with hallways and doors to the floors in the high-rise building, then
> > the fire dept will not connect to the standpipes in the parking garage
> > to fight a theoretical fire in the high-rise...and visa-versa.Just my
> opinion...Mr.
> > Leyton probably could answer this for you.rick matsuda
> >
> >
> >      On Monday, June 29, 2015 10:06 AM, Greg McGahan <
> > [email protected]> wrote:
> >
> >
> >  What about this section?
> >
> > A.7.10.1.1 If a water supply system supplies more than one building or
> > more than one fire area, the total supply can be calculated based on
> > the single building or fire area requiring the greatest number of
> standpipes.
> > For a discussion of use by the fire department of fire department
> > connections, see NFPA 13E
> > <http://codesonline.nfpa.org/a/c.ref/NFC13E/book
> > >
> > , *Recommended Practice for Fire Department Operations in Properties
> > Protected by Sprinkler and Standpipe Systems*.
> >
> > Greg McGahan
> > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> >
> > On Mon, Jun 29, 2015 at 8:01 AM, Pete Schwab <[email protected]>
> wrote:
> >
> > > If the piping supply is connected (common supply piping) then I
> > > would say you have to calculate until you reach 1250 GPM (since the
> > > garage is not sprinklered).
> > >
> > > 7.10.1.2.3* Common supply piping shall be calculated and sized to
> > > provide the required flow rate for all standpipes connected to such
> > > supply piping, with the total not to exceed the maximum flow demand
> > > in 7.10.1.1.5.
> > >
> > > A.7.10.1.2.3 Flow is added at nodes in a standpipe system in
> > > 250 gpm (946 L/min) increments without requiring additional flow,
> > > which might occur from higher pressures at that node (balancing the
> > > system). The common supply piping should be hydraulically calculated
> > > based on the required flow rate [500, 750, 1000, or 1250 gpm (1893,
> > > 2840, 3785, or
> > > 4732 L/min)] for the standpipe system. The calculated pressure for
> > > the standpipe system does not have to be balanced at the point of
> > > connection to the common supply piping.
> > >
> > > It should be noted that the above is my opinion.  It has not been
> > > processed as a formal interpretation in accordance with the NFPA
> > > Regulations Governing Committee Projects and should therefore not be
> > > considered, nor relied upon, as the official position of the NFPA or
> > > its Committees.
> > >
> > > Peter Schwab
> > > VP of Purchasing and Engineering technologies
> > >
> > > Wayne Automatic Fire Sprinklers Inc.
> > > 222 Capitol Court
> > > Ocoee, Fl 34761
> > >
> > > Mobile: (407) 468-8248
> > > Direct: (407) 877-5570
> > > Fax: (407) 656-8026
> > >
> > > www.waynefire.com
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: Sprinklerforum [mailto:
> > > [email protected]] On Behalf Of Greg
> > > McGahan
> > > Sent: Sunday, June 28, 2015 7:49 PM
> > > To: [email protected]
> > > Subject: Re: standpipes in fire separated building
> > >
> > > I will find out tomorrow but this is one lot so I presume it is a
> > > fire wall. The separation into two different buildings appears to
> > > not be necessary per the excerpt from 14. They appear to meet
> > > definition of fire AREA. At least that is indeed what I hope.
> > >
> > >
> > >
> > > Sent from my iPhone
> > >
> > > > On Jun 28, 2015, at 10:21 AM, John Drucker - Home <
> > > [email protected]> wrote:
> > > >
> > > > Greg,
> > > >
> > > > So the garage is classified as a separate building and the two
> > > > systems
> > > are independent ?  Two (2) Hour Rated Wall needs clarification, if
> > > it’s a fire wall or PARTY WALL (See 706.1.1 below) then two separate
> > buildings.
> > > Ask the architect. That’s the key.
> > > >
> > > > 706.1 General. Each portion of a building separated by one or more
> > > > fire walls that comply with the provisions of this section shall
> > > > be considered a separate building. The extent and location of such
> > > > fire walls shall provide a complete separation separation. Where a
> > > > fire wall also separates occupancies that are required to be
> > > > separated by a fire barrier wall, the most restrictive
> > > > requirements of each separation shall apply.
> > > >
> > > > 706.1.1 Party walls. Any wall located on a lot line between
> > > > adjacent buildings, which is used or adapted for joint service
> > > > between the two buildings, shall be constructed as a fire wall in
> > > > accordance with Section 706.
> > > > Party walls shall be constructed without openings and shall create
> > > > separate buildings.
> > > >
> > > >
> > > > Here's the IBC/IFC Code Sections;
> > > >
> > > > [F] 905.2 Installation standard. Standpipe systems shall be
> > > > installed in accordance with this section and NFPA 14.
> > > >
> > > > 905.3.1 Height. Class III standpipe systems shall be installed
> > > > throughout buildings where the floor level of the highest story is
> > > > located more than 30 feet (9144 mm) above the lowest level of the
> > > > fire department vehicle access, or where the floor level of the
> > > > lowest story is located more than 30 feet (9144 mm) below the
> > > > highest level of fire department vehicle access.
> > > > Exceptions:
> > > > 1. Class I standpipes are allowed in buildings equipped throughout
> > > > with an automatic sprinkler system in accordance with Section
> > > > 903.3.1.1 or 903.3.1.2.
> > > > 2. Class I manual standpipes are allowed in open parking garages
> > > > where the highest floor is located not more than 150 feet (45 720
> > > > mm) above the lowest level of fire department vehicle access.
> > > > 3. Class I manual dry standpipes are allowed in open parking
> > > > garages that are subject to freezing temperatures, provided that
> > > > the hose connections are located as required for Class II
> > > > standpipes in accordance with Section 905.5.
> > > > 4. Class I standpipes are allowed in basements equipped throughout
> > > > with an automatic sprinkler system.
> > > > 5. In determining the lowest level of fire department vehicle
> > > > access, it shall not be required to consider:
> > > > 5.1. Recessed loading docks for four vehicles or less, and 5.2.
> > > > Conditions where topography makes access from the fire department
> > > > vehicle to the building impractical or impossible.
> > > >
> > > > [F] 905.4.2 Interconnection. In buildings where more than one
> > > > standpipe is provided, the standpipes shall be interconnected in
> > > > accordance with NFPA 14.
> > > >
> > > > 2014 NFPA-14
> > > >
> > > > 7.10 Flow Rates.
> > > >
> > > > 7.10.1 Class I and Class III Systems.
> > > >
> > > > 7.10.1.1* Flow Rate.
> > > >
> > > > 7.10.1.1.1 For Class I and Class III systems, the minimum flow
> > > > rate for the hydraulically most remote standpipe shall be
> > > > 500 gpm (1893 L/min), through the two most remote 21⁄2 in.
> > > > (65 mm) outlets, and the calculation procedure shall be in
> > > > accordance with 7.10.1.2.
> > > >
> > > > 7.10.1.1.2 Where a horizontal standpipe on a Class I or Class III
> > > > system supplies three or more hose connections on any floor, the
> > > > minimum flow rate for the hydraulically most demanding horizontal
> > > > standpipe shall be 750 gpm
> > > > (2840 L/min), and the calculation procedure shall be in accordance
> > > > with 7.10.1.2.2.
> > > >
> > > > 7.10.1.1.3 The minimum flow rate for additional standpipes shall
> > > > be
> > > > 250 gpm (946 L/min) per standpipe for buildings with floor areas
> > > > that do not exceed 80,000 ft2 (7432 m2) per floor. For buildings
> > > > that exceed 80,000 ft2 (7432m2) per floor, the minimum flow rate
> > > > for the additional standpipes shall be
> > > > 500 gpm (1893 L/min) for the second standpipe and 250 gpm
> > > > (946 L/min) for the third standpipe if the additional flow is
> > > > required for an unsprinklered building.
> > > >
> > > > 7.10.1.1.5 The maximum flow rate shall be 1000 gpm
> > > > (3785 L/min) for buildings that are sprinklered throughout, in
> > > > accordance with NFPA 13, Standard for the Installation of
> > > > Sprinkler Systems, and 1250 gpm (4731 L/min) for buildings that
> > > > are not sprinklered throughout, in accordance with NFPA 13.
> > > >
> > > > Hope that helps,
> > > >
> > > >
> > > > John Drucker, CET
> > > > Assistant Construction Official
> > > > Fire Protection Subcode Official
> > > > Building/Fire/Electrical Inspector Borough of Red Bank Red Bank,
> > > > New Jersey
> > > > Email: [email protected]
> > > > Cell/Text: 732-904-6823
> > > >
> > > >
> > > > -----Original Message-----
> > > > From: Sprinklerforum
> > > > [mailto:[email protected]] On Behalf
> > > > Of Travis Mack
> > > > Sent: Friday, June 26, 2015 11:14 PM
> > > > To: [email protected]
> > > > Subject: Re: standpipes in fire separated building
> > > >
> > > > Look in the IBC and see if that 2 hour wall meets the separation
> > > requirements for a fire separation.
> > > >
> > > > If so, I think you should be able to treat as separate buildings
> > > > for the
> > > standpipe system.
> > > >
> > > > Travis Mack, SET
> > > > MFP Design, LLC
> > > > "Follow" us on Facebook:
> > > > https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> > > > Send large files to MFP Design via:
> > > > https://www.hightail.com/u/MFPDesign
> > > >
> > > > Sent from my iPhone
> > > >
> > > >> On Jun 26, 2015, at 7:15 PM, Greg McGahan <[email protected]>
> > > wrote:
> > > >>
> > > >> I am looking a t a high rise building with 2 stair wells attached
> > > >> to a
> > > >> 7 story parking garage that is not protected. the Parking garage
> > > >> will have two stairwells and be served by automatic dry standpipes.
> > > >> The Parking Garage and the High Rise are separated by a 2 hour
> > > >> rated
> > wall.
> > > >>
> > > >> Question: Do I have to calculate all 4 standpipes simultaneously
> > > >> or can I calc each set separately due to the fire separation
> > > >> between the
> > > two areas?
> > > >>
> > > >> Thank You,
> > > >>
> > > >>
> > > >> Greg McGahan
> > > >> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > > >> 1160 McKenzie Road
> > > >> Cantonment, FL 32533
> > > >> 850-937-1850
> > > >> fax 850-937-1852
> > > >> _______________________________________________
> > > >> Sprinklerforum mailing list
> > > >> [email protected]
> > > >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
> > > >> ri
> > > >> nk
> > > >> l
> > > >> er.org
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
> > > > in
> > > > kl
> > > > er.org
> > > >
> > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
> > > > in
> > > > kl
> > > > er.org
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl er.org _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > > kl
> > > er.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to