In 8.3.2.5(a) a minimum distance of 2'-6" away from diffusers is listed to
allow Ordinary Temp Sprinklers.

8.3.2.5 (9) negates this requirement if the discharge air is less than 100F.

The handbook explains the requirement for the 2'-6" minimum distance and is
being interpreted by one individual as if the intent in the explanation is
that in the event of a malfunction the air could run "hot" (similar to a
car running hot) and therefore the 2'-6" requirement still applies...

I believe the intent is that if the HVAC normally runs "hot" meaning in
excess of 100F the 2'-6" distance must be maintained in order to use
Ordinary Temp heads...