Two things jump top mind. Is the explanatory material in the handbook annex
material verbatim or commentary? In either case they are shalls and so not
code (I presume the "individual" is someone the Wizard bestowed a gold
badge on). Second, no interpretation is supposed to be made up of a list of
what ifs. What if a fire breathing dragon get trapped in the HVAC falls
asleep and notes fire? What if Zombie Hitler fire bombs this buildings air
duct system? What if transients squat in the ducting and start a campfire
to cook their hobo food? People will surely die.

On Wed, Jul 15, 2015 at 6:27 AM, Greg McGahan <[email protected]> wrote:

> In 8.3.2.5(a) a minimum distance of 2'-6" away from diffusers is listed to
> allow Ordinary Temp Sprinklers.
>
> 8.3.2.5 (9) negates this requirement if the discharge air is less than
> 100F.
>
> The handbook explains the requirement for the 2'-6" minimum distance and is
> being interpreted by one individual as if the intent in the explanation is
> that in the event of a malfunction the air could run "hot" (similar to a
> car running hot) and therefore the 2'-6" requirement still applies...
>
> I believe the intent is that if the HVAC normally runs "hot" meaning in
> excess of 100F the 2'-6" distance must be maintained in order to use
> Ordinary Temp heads...
>
>
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to