It's about 15 inches

Ed
Aero Automatic Sprinkler

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Wednesday, July 15, 2015 9:49 AM
To: [email protected]
Subject: RE: ceilings with varying degrees of slope

What's the difference in vertical height between the "flat" ceiling and the 
high point of the "curved" ceiling?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, July 15, 2015 12:33 PM
To: [email protected]
Subject: ceilings with varying degrees of slope

Good morning all,
We have a situation where there are multiple sections of ceilings that start 
off flat/level for several feet and then curve upwards with a pitch that will 
exceed 2:12 at some point in the curve. This situation occurs in a repeating 
pattern over a large section of floor area. At the top of the curve there is a 
small slot that serves as a return air opening. The design intent was to use 
concealed, quick response, ordinary hazard, extended coverage sprinklers 
located in the flat part of the ceiling. The question is "this a flat 
ceiling?". Does the portion of the ceiling that exceeds 2:12 nullify the use of 
the flat ceiling design?
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to